08-07-2011, 06:06 AM #1
Regular Guest
- Join Date
- Aug 2011
- Posts
- 20
Blower Capacity of Trane XV95?
I'm getting conflicting reports about blower capacity of Trane XV95 from contractors. I need a 4-ton AC condenser (considering Trane XR13) according to load calculation. One contractor bid and says that requires the 100K BTU XV95 while another bid the 80K BTU XV95 and says that works fine. Can anyone advise? Where would I find the XV95 blower capacities on the Trane website (I can't find them there)?
If I need the 100K BTU unit for the 4-ton AC, what is the downside if the load calculations say I only need about 70K BTU for heating?
-
08-07-2011, 06:31 AM #2
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,249
http://www.trane.com/webcache/un/fur...7_05012011.pdf
Page 11 seems to provide the necessary info on 4-ton NORMAL air flow requirements.Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
08-07-2011, 07:42 AM #3
Don't oversize the furnace. Trane came out with an 80K XV95 with 4 ton blower just for you
-
08-07-2011, 07:47 AM #4
Regular Guest
- Join Date
- Aug 2011
- Posts
- 20
Thank you very much for the link.
It appears the answer is that there are actually 2 different 80K XV95 models, a *DH2B080A9V3V and a *DH2B080A9V4V. The latter has a larger blower motor (3/4 hp vs 1/2 hp) and is rated for 4-ton AC while the former isn't. So it appears one contractor was not aware of the model with the bigger blower.
The 100 BTU model still appears to have a bit stronger blower according to the charts. Would that help if my ducting was slightly undersized?
-
08-07-2011, 07:52 AM #5
Regular Guest
- Join Date
- Aug 2011
- Posts
- 20
-
08-07-2011, 08:36 AM #6
-
08-07-2011, 12:09 PM #7
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,249
RFQ
Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities


Reply With Quote