OKAY...changed all the solenoids, valves and previously the sensors. It's still tripping on 170 oil temp. It seems now that circuit will not back off. I think something is broken inside the slide valve. It is trying to back off the coil energizes and everything it just doesn't. The Serial # is U96J37008 and the model # is RTAA0804XH01A3D0BFK. All the fans are working and pulling normal amps, the UCM is responding normally it just seems to me that it is the slide valve. I worked it back and forth and saw the difference in pressure at the cavity schrader going from 60 to 200 psi and then to 150 then to 60 again. I tried to service pump down but it just ran and timed out.
Third day on this. Is this slide valve something I should tackle, replace the compressor or call in the factory techs?
-
08-11-2011, 08:11 PM #15
-
08-11-2011, 08:28 PM #16
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 878
-
08-11-2011, 08:31 PM #17
you can also hook a manifold up and apply pressure to loaders and work them, if it does not load its stuck and the head has to come apart.
It's hard to stop a Trane. but I have made one helluva living keeping them going.
-
08-11-2011, 08:34 PM #18It's hard to stop a Trane. but I have made one helluva living keeping them going.
-
08-11-2011, 08:37 PM #19
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 878
It's very unusual for a slide valve to stick on these GP compressors.
-
08-11-2011, 08:42 PM #20You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist