    What's the normal regulator settings for an oxygen and acetlyene torch used for hvac brazing??

  2. #2
    Depends on the size and kind of tip u use. read the paperwork that comes with it. it will tell you all you need to know

  3. #3
    Join Date
    Oct 2005
    Location
    Fairfax, VA
    Posts
    111
    Never more than 15psi for acetylene. Acet regulators are limited to levels below 15 because it's unstable above that ... meaning explosive. Oxygen usually about 40psi.
    The handle valves are adjusted to give a carburizing flame (slight excess acetylene).

  4. #4

    ok

    10-15 acetylene.
    20-30 oxygen

    I normally use 10/20.

    regards,
    kelvin


  5. #5
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,453
    I set for 5 & 10
    Don't know why you would set any higher

    What size tips do you guys use????

    Richard

  6. #6
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    15,960
    Originally posted by bornriding
    I set for 5 & 10
    Don't know why you would set any higher
    Richard

    Ditto !! Same here!!!! always have
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown

  7. #7
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,914
    I set my acetylene for 5 psi and my oxygen for 20 psi. I could probably go lower with the O2 pressure.

    Using higher pressures than that with the tips most people use just makes the flame harder to adjust properly.

    [Edited by mark beiser on 11-11-2005 at 08:42 AM]
    If more government is the answer, then it's a really stupid question.

  8. #8
    Join Date
    Feb 2005
    Location
    small island in the Pacific Ocean
    Posts
    558
    10/20 works well for me

  9. #9
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,548
    anything above 20psig oxygen is a waste. 7-8ace,15-20 oxy
    If everything was always done "by the book"....the book would never change.

  10. #10
    Join Date
    Sep 2005
    Location
    Texas
    Posts
    2,793

    I use

    5 & 15 usually, never give much thought day to day

  11. #11
    Join Date
    Nov 2005
    Location
    South Texas
    Posts
    306
    I just enrolled in a HVAC program and in my safty and install class they are teaching us to use 10 for oxygen and 5 for acetlyene.

  12. #12
    Join Date
    Feb 2005
    Location
    small island in the Pacific Ocean
    Posts
    558
    5-10/10-20 anything is better than a B tank

  13. #13
    Join Date
    Nov 2005
    Location
    Regina, SK Canada
    Posts
    3
    Originally posted by phosgene
    5-10/10-20 anything is better than a B tank

    LOL. True!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event