    lowside 30 high 300 cleaned cond add r-22. low 32 high 380. pulling 9.5 amp Do i have air in the system or is the txv bad.the unit is very old.name plate can not read plate.modle lennox lb-34803bx any help.

  2. #2
    Join Date
    Apr 2003
    Location
    Iowa
    Posts
    763
    Post Likes
    sounds like low airflow across the coil. outside unit sounds like it needs a good cleaning too ...

  3. #3
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes


    Welcome to HVAC TALK.

    Here's something to think about...

    When was the last time you had that unit cleaned and serviced?

    Now you have a problem with the unit. Fuel costs are skyrocketing.

    So why not call in a professional to repair the a/c and look over your heating equipment? While they are there they can clean and inspect your unit to insure a safe living environment for you and your loved ones. Not to mention, having an efficient running system could save you more than the cost of the service.

    What's your safety worth? I'm guessing more than the repair bill.

    Thanks for your understanding.

    (we can't help DIY, due to site rules )

  4. #4
    Join Date
    Nov 2005
    Location
    la.
    Posts
    1
    Post Likes
    thanks for your reply. condenser is claen.and seems i have good air flow across evap.

  5. #5
    Join Date
    Oct 2004
    Posts
    571
    Post Likes

    either way

    Could be a restriction or a bad txv ... either way call a pro.
    a lot of the time I have cust. to work on a system and end up
    spending more trying to fix it than what I charged them to fix it.



  6. #6
    Join Date
    Nov 2005
    Posts
    4
    Post Likes
    with the high and low pressures the way you describe them it sounds like a problem with the txv.. in which you should contact a certified repair man to fix... If it was a airflow problem at the evap coil, both presurse would be lower than normal...

  7. #7
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Originally posted by yogibear70461
    thanks for your reply. condenser is claen.and seems i have good air flow across evap.
    What is your airflow? (Acutal CFM)

    Originally posted by idahotech
    If it was a airflow problem at the evap coil, both presurse would be lower than normal...
    Not if it's overcharged to compensate.

    Superheat is the only way to know if a TXV is functioning and there are a few other things that must be confirmed before you can even get to that point.