recently I encounter another voyager with similar set of problems, 2 stages RTU, both evaporators starving, new compressors, superheat way up there with high supcooling, after changing the orifices to TXV's everything went back to normal but the orifices looked clean as whistle, wonder if the crap blocking them was moved while recovering or... ?? who knows what a piss poor design that was.
-
07-31-2011, 08:20 AM #15
Regular Guest
- Join Date
- May 2006
- Posts
- 18
Could be an oil logged evaporator.
-
07-31-2011, 09:06 AM #16
Guest
- Join Date
- Apr 2005
- Location
- where the beer flows like wine
- Posts
- 2,871
-
07-31-2011, 11:00 AM #17
Professional Member
- Join Date
- Nov 2006
- Location
- North Carolina
- Posts
- 125
Did you put a oversized dryer in it or the little ones they come from the factory with, also did you nitrogen purge while brazing in the new orifice header?
-
08-05-2011, 03:30 PM #18
Regular Guest
- Join Date
- Apr 2010
- Location
- Central Minnesota
- Posts
- 18
Returned today to do a bit more troubleshooting...long story shot, same type of numbers and no conclusions. Pulled blower belt and all circuits looked to be feeding ok. Service manager told me to go ahead and order a txv kit - our parts ordering guy said they didnt have one for this model.
M/N: YCD090C3H0BC
S/N: J41102181F
-
08-05-2011, 05:30 PM #19
Guest
- Join Date
- Apr 2005
- Location
- where the beer flows like wine
- Posts
- 2,871
Dont buy from Trane their parts guys are on crack. go to United get a 8 tons Sporlan TXV, matching distributor and a roll of tubing for the octopus, if you dont feel like doing it the hard way, Sporlan can make the kit for you, talk to your local sales rep, http://www.sporlanonline.com/unitedstates.htm
-
08-05-2011, 10:05 PM #20
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 927
Trane doesn't sell a TXV kit for these units. This is something your going to have to fabricate yourself. Follow Hvacpope's advise and buy the individual parts. And don't let your parts ordering guy at the shop order your parts because this is something that he will screw up unless he's an experienced tech. You'll probably need to go into the supply house yourself and match up these parts.
-
08-05-2011, 10:28 PM #21
Professional Member
- Join Date
- Dec 2009
- Posts
- 83
Did you weigh in new 22 or the stuff you pulled out? Also have you looked at the charging chart to see where you stand with that?
-
08-06-2011, 09:54 AM #22
How do you know what size distributer and tube diameter you need for that specific application? Are the distributers rated in capacity? THen just buy the Tube that goes with it?
Gotta have the right tool for the job!
Where is all the stuff MADE IN THE USA?
"Thats what we do Troy. Incredible, Invisible, Imbelivable things. We are an Unseen, Unknown, Unvincible fraternity of craftsman.."
-
08-06-2011, 10:28 AM #23
Guest
- Join Date
- Apr 2005
- Location
- where the beer flows like wine
- Posts
- 2,871
there are calculations involved in selecting the tubing, distributor and orifice.
basically knowing the unit tonnage and the amount of evaporator circuits will be enough information for the Sporlan rep. to size the rest accordingly.
I've done the calculations manually and somehow my results always differ from my local rep. he uses a sizing software, I always go with what he recommends.
In this particular case I believe is a 8 tons rtu with 9 circuits evap. and the tubing for the octopus 3/16, make sure to braze with safety-silv 56 or 45% and flux, staybrite 8 would also do the trick, I prefer the safety silv56
read this. http://www.jandrewschoen.com/sporlan/20-10_062009.pdf
-
08-06-2011, 01:00 PM #24
What are the compressor amps doing in all this? Are they close to full load?
-
08-06-2011, 09:39 PM #25