    I have a York Furnace in the Attic. Using a Honeywell rth7500d thermostat.

    The system is set to heat
    Kick the fan to ON and the AC kicks on.

    Double checked the wires on the thermostat. Crawled up in the attic and look there to. Everything is wired as it should be.

    Ideas?

    Thanks

    Steve


  2. #2
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,001
    Post Likes
    So does the A/C run when the t-stat fan switch is set to on or when the blower kicks in for heating?

    Make sure that Y (wire) is not making contact with G (wire)anywhere along the control circuit.

    Other than that, there's no much you can do. Turn off the A/C disconnect to avoid compressor damage and call a technician.

  3. #3
    Join Date
    Aug 2001
    Posts
    329
    Post Likes
    there's a short somewhere between g - y, maybe the wire is pinched somewhere. check for continuity between g-y.

  4. #4
    Join Date
    Nov 2005
    Posts
    2
    Post Likes
    If Heat kicks on the AC does NOT kick on. I should clarify more.

    Regardless if the system is in Heat or Cool and I just switch the Fan to ON instead of AUTO the AC will kick on. I just want to recurculate the air in the house without Heat or AC on.

    Steve

  5. #5
    Join Date
    Aug 2001
    Posts
    329
    Post Likes
    that's because in heat mode with your thermostat only r-w are closed.

  6. #6
    Join Date
    Jan 2003
    Posts
    959
    Post Likes

    short, short

    This is a simpel one..

    you have a short between green and blue (G and Y)
    This means both are toching.
    Check at furnace to see what going on with green wire.
    You might have a jumper on g amd y at furnace.

    A simple temporary fix put green wire on y. you want have high speed fan but your ac will not come on untill you call for it.