    Sorry but what does rtu stands for? The guy that designed the supermarket he put the return duct near the open freezers. Do you think that could be a problem too?
    Air curtains are very common on grocery stores.
    They help keep the conditioned air contained within the building as the doors open and close. They also help with keeping bugs out of the building.
    I understand the bug part & can understand keeping conditioned air in ... its use for keeping unconditioned air out is what was sounding off
    RTU stands for "roof top unit". In your case it refers to the York 25-ton split system.
    Madison, WI/Cape Coral, FL
    Reheat without making sure that all of the a/c cooling coils are as cold as possible is spinning your wheels. Cooling coils operating at <40-45^F are the starting point. The dew point of the air inside the store will be 5^F-10^F above the a/c coil temp provided infiltration is under control. Reheat only work with extremely cold coil a/c. For situations where there not free reheat, use high capacity, high efficiency dehumidifiers like the Quest, Ultra-Aire, Hi-E Dry. These unit remove 6-8 lbs. of moisture per KW and provide free reheat.
    Most important first to get the a/c operating with the coldest coil possible. Slow the air flow is a way to get the coil temp needed.
    Regards TB
    Mar 2011
    The unit has a return dry bulb of 70 f and a supply dry bulb of 58 f.
    Slow the air down a little.