Update: thanks to the excellent replies on this thread. Absolutely useful and great education for me and hopefully helpful to others in future.
Root cause found to be crossed wiring at outdoor unit. Tstat was signaling for compressor to run at low and turning fan to low. However, outdoor unit was not coming on until tstat signaled for high.
Now at 42% to 45% humidity. Doesn't come on very often, when it does it's on low - very gentle air flow. No problem hold temp at 78 at 100+ outside. No sticking to floors.
One observation: when the unit was running the fan w/o compressor we noticed that our normally blast furnace like upstairs was almost same temp as down stairs. It was dramatic change. This tells me that the classic upstairs/downstairs problem might be solved with a more continuous air flow. However, it would have to be done without humidity. It will take a few days to see how things are now that unit is working correctly.
I asked about comfort-r setting, tech said he didn't set it. He wanted to try things without it.
One last question - thanks for indulging me.
What the heck is comfort-r exactly? When unit is in comfort-r what does it do that is different than when it is not in comfort-r?
-
08-02-2011, 12:01 PM #29
Professional Member
- Join Date
- Aug 2011
- Location
- San Jose California
- Posts
- 85
-
08-02-2011, 12:56 PM #30
Regular Guest
- Join Date
- Nov 2003
- Posts
- 19
Ack! I read that earlier and then completely pushed it out of my brain.
Perfect description. Thanks Skippedover and freon22.
-
08-02-2011, 10:06 PM #31
Get the Comfort-R turned on. That will get the coil colder, and help with the humidity control.
-
08-03-2011, 01:50 PM #32
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
I always turn on the comfort r on the 16 I
-
08-05-2011, 10:36 PM #33
Regular Guest
- Join Date
- Nov 2003
- Posts
- 19
Thanks very much for the replies - the tech didn't set comfort-r. The unit is running really well right now. Austin has lower humidity than most place in south, but right now it is like 102 to 105F outside so maybe its the heat not the humidity for a change!
You can read about our results with the unit here. We are so impressed right now, and it is one of those rare times things work better than you hope, I am afraid to mess with it!
http://hvac-talk.com/vbb/showthread.php?t=894702&page=2
My experience seems to show that two stage can work well even in hotter than h#ll Texas. Hope this technology comes down in price.
-
08-06-2011, 01:26 AM #34
I don't know why Comfort R is not the default setting on those variable speed air handlers. It should be. IMO.