    York YCAS0150 problem

    I have a York screw chiller where circuit 1 compressor locks out on high discharge temp-runs 20 min to 1 hour. Have checked charge, subcooling superheat etc. all fans operational. History log shows that the capacity control is at or near the highest step 73 to 75 but the current is only 57 to 60% of full load. I suspect the slide valve is stuck and not opening fully.
    Does anyone know the checkout procedure for this slide mechanism, solenoid valve etc.

    Thanks Coolairman

  2. #2
    Join Date
    Oct 2009
    Location
    God's country - Shenandoah Valley, VA
    Posts
    1,764
    Post Likes
    Have you confirmed the accuracy of the sensor?

  3. #3
    Join Date
    Dec 2002
    Location
    Titusville Florida
    Posts
    342
    Post Likes
    check your high pressure transducer and cable, Had same problem. trans ducer would not bring fans on all of the time.

  4. #4
    Join Date
    Dec 2002
    Location
    Titusville Florida
    Posts
    342
    Post Likes
    Here's your manual
    Attached Files Attached Files

  5. #5
    Join Date
    May 2003
    Location
    Charleston SC
    Posts
    172
    Post Likes
    Thread Starter
    Thanks Sabre

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •