    Question about reach in fridge by True Manufacturing

    Hi I have a question I'm trying to charge a reach in but was wondering what the temperature inside the box should be compared to the evap coil temperature. The evap coil temperature is 35 F so what should the ambient inside the box be for a proper charge?

  2. #2
    Join Date
    Feb 2009
    Location
    Under a bridge if things don't pick-up
    Posts
    397
    Post Likes
    40
    Don't go away angry... Just go away.

  3. #3
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    1,642
    Post Likes
    First, clean the condenser.
    Then, check that the doors are closing correctly and that the gaskets are ok.
    Then, if it still doesn't work, either call a qualified tech or send the unit to the junk pile and buy a new one.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,233
    Post Likes
    The true cabinets that I've seen are critically charged.

    I pull the charge, evacuate and weigh it back per nameplate.

  5. #5
    Join Date
    Jan 2010
    Posts
    8,100
    Post Likes
    Quote Originally Posted by HoneyDo View Post
    40
    40* @ a 5*TD or 45* @ 10* TD

  6. #6
    Join Date
    Aug 2007
    Posts
    12
    Post Likes
    35 deg sst seems kind of high! Evap temp of 25 with 10deg td seems more appropriate

  7. #7
    Join Date
    Jul 2011
    Location
    northern Minnesota
    Posts
    36
    Post Likes
    i agree with jpsmith1cm, don't forget about the juice weight in you hoses. battled one for a day or two, did exactly what he suggested, runs like a timex now. another clown topped it off, off the ampmeter, 4 oz overcharged.. and all it probably needed was a good cleaning

  8. #8
    Join Date
    Dec 2008
    Location
    Nor•Cal
    Posts
    221
    Post Likes
    Quote Originally Posted by budz View Post
    35 deg sst seems kind of high! Evap temp of 25 with 10deg td seems more appropriate
    Reachin = 20 td. Walkin = 10 td.

  9. #9
    Join Date
    Jul 2011
    Location
    Virginia
    Posts
    41
    Post Likes
    Thank you so much for the help, in this field it is true we all cannot know it all. thanks again.