    Bad Compressor or compressors?
    CARRIER
    MODEL# 48TJE012---511GA
    SERIAL# 1297G30820
    TEN TON TWO STAGE RTU
    STAGE ONE OPERATION NORMAL 17.5 AMPS
    STAGE TWO VOLTAGE NO OPERATION OHM'D S,R,C WINDINGS FOUND OL ON ALL.
    PLAN IS TO REPLACE COMPRESSOR 2. WOULD THERE BE REASON TO REPLACE COMP 1 EX: ACID FROM COMP 2 BURNING OUT
    BEAR WITH ME I'M FAIRLY NEW TO THE COMMERCIAL HVAC
    THANKS
    Southeastern Pa
    I would do one only. No interconnection between stages.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Southeastern Pa
    And don't use caps when posting. Thanks.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Anytown USA
    Was the compressor shell really hot when you ohmed the windings, or was it cold?
    Oct 2007
    Austin Texas
    It could have been out on thermal OL. Were any of the winding shorted to ground? I'm assuming if you have S R C windings that it is single phase, and so was the capacitor checked?
    Nemo me impune lacessit.
    How much blood do I have to bathe in to get clean?
    Don't look down on anyone unless you're helping them up.
    The Hot South
    I don't ever think I've seen a 10 ton single phase package unit. I'm assuming this unit is 3 phase and your ohming across L1, L2, & L3. Most of the times the terminals are marked R,S,&C in addition to L1, L2, & L3. As previously posted, are you sure the thermal overload wasn't opened? You would have to have at least 2 windings open for all 3 legs to show open if the overload was closed plus you would more than likely show a ground. Was the compressor hot when you checked it?
    Southeastern Pa
    The OP is just confused because CSR is still shown along with T1, T2, and T3. The 012 is a three phase unit.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jun 2011
    it was cold. i removed all the wires to it, so any capacitor would be out of the loop. overload was closed.
    The Hot South
    Just curious.....how did you determine the overload was closed?
    Southeastern Pa
    There are no caps in the compressor wiring. Three phase compressors don't use them or need them.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules: