    Need Damper Linkage Drawing

    I Have Five Carrier 5 Ton RTUs that have Manual set fresh air dampers, I need to make them automatic. IE when the fan is off, they close. Carrier only offers an Economizer for these units $$$. I'm thinking about using Honeywells M847D1012 Damper motors, and I'd like to have any linkage drawings so I can figure out how to fabricate something. There is no Rod that I can use to open the damper, and I'm thinking on the lines of pushing the damper open, much in the way a door closer would work.

  2. #2
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    1,629
    Check back with Carrier, they offer a two position damper assembly for most smaller units at less $$ than an economizer. It will probably be less expensive to use them rather than spending your valuable time fabricating something.

    Kevin
    "There are 10 types of people in the world.. those who understand binary, and those who don't."