    I just purchased a 100 year old home here in Louisville Kentucky. The furnace was shot. There was no duct work for the second floor. I have removed the drop ceilings and have room to run new duct work for the second floor.
    I want to install a new heating and air system in the house. I intend to be here for a few years maybe more.
    I have gotten mixed information on what components to use.
    Some say use a spit system, a heat pump with a gas furnace others say heat pump only and still others say gas funace and central air unit.
    On the gas funace end I can get a pretty good deal on American Standards top of the line furnace the Freedom 90 Comfort R from a friend of mine that does commercial work.
    Just to get a second opinion I had a contractor from my area come over and give me a bid. He said that particular furnace would be a waste in my house, he recomended a Rheem Classic 90 Plus. He recomended a 14 sear air conditioner were the other recomended a 14 sear heat pump.
    The home is a 1500 sq ft two story shoot gun house that I am insulating and replacing the windows with two pane.
    I really am at a lose here. Our local gas and electric company just raised gas rates by 64% and I need to get this system in before it gets much colder. I want to do it right, but don't want to waste my money on the best if it won't make a difference.
    Please help.

  2. #2
    Join Date
    Oct 2005
    Location
    Quincy, Il
    Posts
    24
    If you can get a deal on the American Standard then go for it. The other guy said that it would be a waste because he wants commision. The company I work for sells american standard equipment, and in the 6 or so years that they have been installing it they have only had one warranty service call. Plus, they come with a pretty good warranty

  3. #3
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,376

    Hmm No that's OLD !

    Originally posted by markgrmc
    I just purchased a 100 year old home here in Louisville Kentucky.
    ...
    He recomended a 14 SEER air conditioner were the other recomended a 14 SEER heat pump.

    The home is a 1500 sq ft two story shoot gun house that I am insulating and replacing the windows with two pane.

    ... company just raised gas rates by 64% and I need to get this system in before it gets much colder. Please help.
    For starters,
    Gas Rate ......$ _.__ MCF
    Electric Rate .$0.___ / kW
    Did you check WINTER rate specifically for Heat Pump?

    Help yourself by helping others
    obtain a more specific 'reference point'.

    I don't know what a shoot gun house is.

    1,500 S.F. and Louisville are good info.
    800 [ ? ] S.F. Down stairs
    ?___ S.F. Glass North ___ S.F. Glass South
    ?___ S.F. Glass East ___ S.F. Glass West

    700 [ ? ] S.F Up...stairs
    ?___ S.F. Glass North ___ S.F. Glass South
    ?___ S.F. Glass East ___ S.F. Glass West

    Ceiling_ R-value 19, 30 or 38 ?
    Walls __ R-value 11, 13 or 19 ?

    Infiltration ___ 100-year old house
    Has any testing been done to determine leakage?

    Windows S.H.G.C. ____ U-value ____

    W.A.G.
    ~50,000 BTUH Heating
    ~25,000 BTUh Cooling

    3 MIGHT be appropriate .. but
    Who knows exactly??

    TRANE Heat Pump model ( or equal)
    4TWX 6036 /4TEE3F040 with 10 or 15 kW electric strip

    .... BTUh for Heat Pump & Coefficient of Performance
    O.A.T.
    17'F _ 22,200 BTUh C.O.P. 2.96
    35'F _ 25,920 BTUh C.O.P. 3.28
    47'F _ 33,200 BTUh C.O.P. 4.06

    H.S.P.F. 9.2 SEER 17.

    Recommend that 2-story be zoned.

    NEXT:
    KY Temperature bin data reviews.


    [Edited by dan sw fl on 11-03-2005 at 10:54 PM]
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  4. #4
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    6,376

    Thumbs up KY Bin Data

    Ft Knox
    Temp Hours
    100 0
    95.. 5
    90.. 78
    85.. 278
    80.. 499
    75.. 678
    70.. 941
    65.. 858
    60.. 777
    55.. 653
    50.. 624
    45.. 593
    40.. 616
    35.. 600
    30.. 608
    25.. 399
    20.. 248
    15.. 137
    10.. 75
    5... 42
    0. 30
    -5 7
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event