    Question

    I came across my first oil fired furnace today, and I have to be honest I do not know much about them. To the best of my knowledge there are not many here, none of the techs I have talked with have ever seen one here. What are some signs of the system not running correctly? How do they differ from a Natural Gas furnace?

    Thanks for any information, 98% of heating equipment I work on is HPs or Strip heat.

  2. #2
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    walk away from it until you have had training.

  3. #3
    Join Date
    Oct 2005
    Location
    Quincy, Il
    Posts
    24
    Post Likes
    They're really not that difficult. I taught myself how to work on them in the military. That is all they had was oil fired furnaces, dryers, and hot water heaters. the components aren't to much more diffrent then natural gas furnace. You have electrodes (to ignite), cad-cell flame sensor. Big transformer for spark, ususally 100,000 volts, fuel pump set @ 110-120 psi mounted on burner assembly. You may run into a stack switch or something like that. I know that nozzles have a screen on them, and should be replaced every year with the exact replacment. Number on nozzle indicates number of gallons of fuel burned per hour. Electrodes tend to gum up and prevent proper ignition. Also electrode gap is important. Don't remember the exact gap but I think it is 1/8 in. Same with cad-cell. Needs to be cleaned. May be more to the civilian models. I've only worked on mainly military models. Best thing for you to do is get a book that covers oil-fired furnaces.

  4. #4
    Join Date
    Jan 2003
    Location
    Panama City, FL
    Posts
    53
    Post Likes
    Thread Starter
    I agree with you, that is what I did. The home owner was a little upset, she told me my company was the only company that agreed to take a look at it. The service manager of the company I work at does not anything about oil fired, so there is not much anyone could say to me. I have a little information on this type, but not enought that I would feel comfortable working on them.

  5. #5
    Join Date
    Oct 2005
    Location
    Quincy, Il
    Posts
    24
    Post Likes
    What problem are you having with it?

  6. #6
    Join Date
    Jan 2003
    Location
    Panama City, FL
    Posts
    53
    Post Likes
    Thread Starter
    Nothing that I know of, customer just wanted the system checked out. From what you wrote there are several things that need to be done to these furnaces. I will study about these, I would like to know how to work on them.

  7. #7
    Join Date
    Dec 2002
    Location
    Rochester, MN
    Posts
    5,307
    Post Likes
    They are not really that bad.. Do some reading up on it..

    How or where does the customer get oil for it? The oil company has a service tech for oil equipment??

  8. #8
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    Originally posted by mister freeze
    .... the components aren't to much more diffrent then natural gas furnace. You have electrodes (to ignite), cad-cell flame sensor. Big transformer for spark, ususally 100,000 volts,
    Um, no...more like 10,000 volts for old style transformers, 14K volt with the new solid state ignitors.

    Originally posted by mister freeze
    .... fuel pump set @ 110-120 psi mounted on burner assembly.
    Um, no....more like 100 psi with older burners, 140 or more psi with new oil fired equipment.

    Originally posted by mister freeze
    .... You may run into a stack switch or something like that.
    Um, ditto.....no stack switches anymore, solid state equipment has long since replaced mechanical warp switch safety resets.

    Originally posted by mister freeze
    .... Electrodes tend to gum up and prevent proper ignition.
    Nope...electrodes that gum up are signs of big problem elsewhere, electrodes barely even wear out nowadays.

    Originally posted by mister freeze
    .... Same with cad-cell. Needs to be cleaned. May be more to the civilian models.
    Nope....a cad cell that needs cleaning is sign of a big problem elsewhere. Cad cells stay clean with proper ignition and a clean boiler.

    Originally posted by mister freeze
    .... Best thing for you to do is get a book that covers oil-fired furnaces.
    I haven't seen a book available to homeowners that would present MODERN oil burner repair acceptably. The books you find are soooo outdated, it's laughable. Best thing for you to do is call a tech...instead.


  9. #9
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    I don't get to chime in on these threads very often, so excuse me for taking the chance. Shorty, you are to be commended for seeking knowledge on something that you are not familiar with. I think that everyone on this site would agree that it it is much...MUCH wiser to back away and think about or even seek out information before diving into something head first. Here is the problem: t527ed makes a valid point but what can you do? You said it yourself, your SERVICE MANAGER doesn't know anything about oil fired machines yet YOU are expected to...that is what being a service tech is about a lot of times. It alays makes me laugh when I think about the bs that people will put up from doctors and then they hold HVAC techs to some standard that is unattainable. I don't know how long you have been a service tech, but I can't count the times that I have arrived on a jobsite and seen equipment that I didn't know existed or even what it was supposed to do and the maintenance or plant engineer expected a factory rep. Oh well, I guess that we have to do the best that we can.
    I am getting away from the topic here. If you don't have many furnaces , and i suppose living in Florida, you wouldn't see many like you said, there is no need to get all tooled up for oil work. However, if you want to do a fair job of servicing this machine, you should really take a look at how it is burning. If you plan on ever servicing any boilers (an you should always be looking at advancing) ther is a fair chance that you will need a smoke tester, if they are oil fired. Maybe you could justify getting one through the shop and test the amount of smoke this burner is making. It sounds like you are doing some research and you should go to the Bacharach website and read a little about combustion.
    Take care and good luck.

    r404a

  10. #10
    Join Date
    Jun 2003
    Location
    New Hampshire
    Posts
    2,752
    Post Likes
    Originally posted by t527ed
    walk away from it until you have had training.
    I agree. There are too many things that can go wrong.
    I wouldn't work on a freezer either. If you don't have the parts to replace that need replacing and Bacharach oil tune up kit, and the know how to be sure it is running correctly, walk away.
    If someone is delivering oil to them there must be someone out there that works on oil fired units.

    [Edited by oil lp man on 11-02-2005 at 06:03 AM]

  11. #11
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes

    Thumbs up R elative A ccuracy

    [QUOTE]Originally posted by casturbo
    [B]
    Originally posted by mister freeze
    .... the components aren't to much more diffrent then natural gas furnace. You have electrodes (to ignite), cad-cell flame sensor.

    Big transformer for spark, usually 100,000 volts,
    Um, no...more like 10,000 volts for old style transformers, 14K volt with the new solid state ignitors.
    ................

    What's a 0 here or there?

    EarthQuake of 80 on the Richter Scale ( 8.0 )
    Hurricane of CATegory 50 (5 )
    Snowfall of 150 Inches ( 15 )

    Speed Limit 700 MPH ( 70 )

    I little more precision may be needed. L.O.L.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  12. #12
    Join Date
    Jan 2003
    Location
    Panama City, FL
    Posts
    53
    Post Likes
    Thread Starter
    I am not sure if the company that supplies the oil has someone to check the furnace. The home owner told me the the supplier said she needed someone to check the unit out, to make sure everything is alright this winter. I know that heating oil is very rare here, if gas is used it most of the time is natural. When I was in HVAC training, there was a section on oil fired, but it was removed because the teacher tought it was not nessary.

    Thanks for the replys

  13. #13
    Join Date
    Jul 2005
    Posts
    717
    Post Likes
    Shorty 6801; just out of curiousity, how long has it been since this oil furnace was installed?
    Normally a furnace/burner should be serviced (tune-up) annually.
    And who, or where is the "tech" that originally did the initial setting-up?
    btw, i,m sure glad a poster or two corrected Mr freeze on his erroneous info. Maybe he ought to join Shorty in learning more about oil heat,etc

    ps;That oil supplier must be doing a flourishing business with only one or two customers in the whole area... lol

  14. #14
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,212
    Post Likes
    I agree with the oil man. We service about 2000 oil customers and we are 1 of 2 companies that service oil fired equipment. The other companies here send that kind of work our way. There is so much to know about oil burners you would be surprised. The wrong nozzle pattern will frighten you when it lights off. Wrong air fuel mixture can soot up a unit in a matter of hours. Stack switch or primary control, pump settings, filters, pump screens it is a fairly long list of things you need to know and have just to service one burner. The bacharach kit costs about $ and if you don't use it or a similar kit you are doing it wrong and many here do it wrong. Unless this type of work is going to expand for you I would beg it off on another. Beckett has very good courses on this if your interest grows. Good luck.

    [Edited by Lusker on 11-21-2005 at 08:16 AM]
    Proud supporter of Springfield Millers and Oregon Ducks.

  15. #15
    Join Date
    Oct 2005
    Posts
    927
    Post Likes

    Thumbs down oil

    If you take that apart and you say you no little about the set up you will be flying in some on from this site to put back all the $$$##. Think about the call at 3am asking for help.

  16. #16
    Join Date
    Oct 2005
    Posts
    16
    Post Likes
    Where are all you guys from that havent had much experience with oil fired? Just curious because my area seems to be more oil than gas heating used, in the northeast that is.

  17. #17
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,212
    Post Likes
    Originally posted by blown67
    Where are all you guys from that havent had much experience with oil fired? Just curious because my area seems to be more oil than gas heating used, in the northeast that is.
    Eugene, Oregon. Oil is fading fast with gas and heat pumps taking over.
    Proud supporter of Springfield Millers and Oregon Ducks.

  18. #18
    Join Date
    Oct 2005
    Posts
    16
    Post Likes
    My burnham boiler is about tens years old and now that my house is mostly insulated top to bottom, as opposed to none at all when I bought it, I feel will be oversized for my needs, my question is advantages price/mechanical wise when I replace to go oil or gas. I have no gas in my neighborhood so it would be lp, and would have to have it delivered same as oil. I still want to stay with the hot water base because I only have one room left to put new baseboard in. My last 2 houses were gas hot air, not really crazy about the hot/cold cycling but they were not 2 stage or even close to top of the line models, it always seemed like it was hot or cold. Also wife always said it was to dry, even after the humidifer was added.....

  19. #19
    Join Date
    Jan 2005
    Location
    Massachusetts
    Posts
    514
    Post Likes
    Delayed ignitions and lots of soot if not set up correctly. I try to stay away from gas if I can because I just dont do enough of it. I recomend the same.

    Originally posted by shorty 6801
    How do they differ from a Natural Gas furnace?

  20. #20
    Join Date
    Aug 2003
    Posts
    125
    Post Likes
    Just go to the north east, especially Philadelphia suburbs. Oil burners rule the roost here.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •