Thread: I cannot FIND THIS LEAK!!!!
-
07-27-2011, 08:27 PM #27
Regular Guest
- Join Date
- Apr 2010
- Posts
- 75
This, by far, was the craziest thing I've ever worked on.
Ok, so more dye was put in the system. Went back the next day to find the evap full of dye. Perfect, the evap is shot. Just before I'm about to condemn it, something tells me to check around a little more - why is there dye on the floor of the freezer? And maybe I've been watching CSI too much, because I see - a spray pattern on the evap?
Pump 'er down again, ramp the nitrogen to 300#. All the sudden PSSSSSSS - out of a braze joint right by the solenoid that runs behind the evap - spraying a pretty picture. Drop the pressure to 200 and literally NOTHING. Spray soap shows tiny bubbles. Ramp it back up to 300, blows the soap off the joint. I've never seen anything like this in all my years.
Rebraze joint, vac and recharge - returned two days to a full sight glass.
Perplexing, for sure.
-
07-27-2011, 08:30 PM #28
Professional Member*
- Join Date
- Jun 2008
- Location
- NW Florida
- Posts
- 701
Got a better one.
Had a unit in county jail house kept loosing about half the charge in three days. No leaks any where. Marked caps. Sure enough next time out low again caps had been moved. Talked to seargeant at jail I put Uv dye in system. Seems jail house had a black light. Poor guy got three months added to sentence. He only had three weeks left.
-
07-27-2011, 08:34 PM #29
Professional Member*
- Join Date
- Jun 2008
- Location
- NW Florida
- Posts
- 701
-
07-27-2011, 09:03 PM #30
Regular Guest
- Join Date
- Jul 2011
- Location
- space coast, florida
- Posts
- 13
im with you was sweating in a valve on a wlkin someone closed the door on me had some vapor trapped in the line almost puked. people are sick
-
07-28-2011, 05:39 AM #31
Regular Guest
- Join Date
- May 2011
- Posts
- 17
No refrigerant detector for the freezer???
c
-
07-28-2011, 07:42 PM #32
-
07-28-2011, 07:47 PM #33
-
07-28-2011, 08:41 PM #34
Professional Member*
- Join Date
- Jun 2008
- Location
- NW Florida
- Posts
- 701
-
07-30-2011, 11:17 AM #35
Regular Guest
- Join Date
- Jul 2011
- Location
- Virginia
- Posts
- 12
Could be a king valve has happened to me before
I had an issue where one of my king valves was bleeding off refrigerant once the pressure got about 250 psi. I would check the valve and see if it bleeds once the pressure on your nitrogen bottle starts to get around 250 + just close the valve completely and see if it holds. If it does than it's definetley the valve.
-
07-31-2011, 02:08 AM #36
-
07-31-2011, 06:34 AM #37
Professional Member*
- Join Date
- Jun 2008
- Location
- NW Florida
- Posts
- 701
-
07-31-2011, 10:53 AM #38
-
07-31-2011, 04:23 PM #39
Professional Member*
- Join Date
- Jun 2008
- Location
- NW Florida
- Posts
- 701


Reply With Quote
.
.