  1. #27
    Join Date
    Apr 2010
    Posts
    94
    This, by far, was the craziest thing I've ever worked on.

    Ok, so more dye was put in the system. Went back the next day to find the evap full of dye. Perfect, the evap is shot. Just before I'm about to condemn it, something tells me to check around a little more - why is there dye on the floor of the freezer? And maybe I've been watching CSI too much, because I see - a spray pattern on the evap?

    Pump 'er down again, ramp the nitrogen to 300#. All the sudden PSSSSSSS - out of a braze joint right by the solenoid that runs behind the evap - spraying a pretty picture. Drop the pressure to 200 and literally NOTHING. Spray soap shows tiny bubbles. Ramp it back up to 300, blows the soap off the joint. I've never seen anything like this in all my years.

    Rebraze joint, vac and recharge - returned two days to a full sight glass.

    Perplexing, for sure.

  2. #28
    Join Date
    Jun 2008
    Location
    NW Florida
    Posts
    713

    Got a better one.

    Quote Originally Posted by kelvin View Post
    Nice trick .
    Had a unit in county jail house kept loosing about half the charge in three days. No leaks any where. Marked caps. Sure enough next time out low again caps had been moved. Talked to seargeant at jail I put Uv dye in system. Seems jail house had a black light. Poor guy got three months added to sentence. He only had three weeks left.

  3. #29
    Join Date
    Jun 2008
    Location
    NW Florida
    Posts
    713

    High pressure leak.

    Quote Originally Posted by Kevin_1963 View Post
    This, by far, was the craziest thing I've ever worked on.

    Ok, so more dye was put in the system. Went back the next day to find the evap full of dye. Perfect, the evap is shot. Just before I'm about to condemn it, something tells me to check around a little more - why is there dye on the floor of the freezer? And maybe I've been watching CSI too much, because I see - a spray pattern on the evap?

    Pump 'er down again, ramp the nitrogen to 300#. All the sudden PSSSSSSS - out of a braze joint right by the solenoid that runs behind the evap - spraying a pretty picture. Drop the pressure to 200 and literally NOTHING. Spray soap shows tiny bubbles. Ramp it back up to 300, blows the soap off the joint. I've never seen anything like this in all my years.

    Rebraze joint, vac and recharge - returned two days to a full sight glass.

    Perplexing, for sure.
    Good head scratcher. Now you need to go to church and repent for all the foul language you used on that unit. lol

  4. #30
    Join Date
    Jul 2011
    Location
    space coast, florida
    Posts
    13
    im with you was sweating in a valve on a wlkin someone closed the door on me had some vapor trapped in the line almost puked. people are sick

  5. #31
    Join Date
    May 2011
    Posts
    17
    No refrigerant detector for the freezer???

    c

  6. #32
    Join Date
    Jun 2005
    Posts
    171
    Quote Originally Posted by Kevin_1963 View Post
    Drop the pressure to 200 and literally NOTHING. Spray soap shows tiny bubbles.
    And you told us it held the 200#.
    If we evolve from the monkey then why are there still monkeys.

    GOD Bless America.

  7. #33
    Join Date
    Jun 2005
    Posts
    171

    Working at the County Jail

    Quote Originally Posted by meoberry View Post
    Had a unit in county jail house kept loosing about half the charge in three days. No leaks any where. Marked caps. Sure enough next time out low again caps had been moved. Talked to seargeant at jail I put Uv dye in system. Seems jail house had a black light. Poor guy got three months added to sentence. He only had three weeks left.
    I worked at the county jail also. One of the reason we cannot served at the Jury. We might ended up seeing each other at the jail .
    If we evolve from the monkey then why are there still monkeys.

    GOD Bless America.

  8. #34
    Join Date
    Jun 2008
    Location
    NW Florida
    Posts
    713
    Quote Originally Posted by kelvin View Post
    I worked at the county jail also. One of the reason we cannot served at the Jury. We might ended up seeing each other at the jail .
    I hope not from the wrong side of the bars.lol

  9. #35
    Join Date
    Jul 2011
    Location
    Virginia
    Posts
    41

    Could be a king valve has happened to me before

    I had an issue where one of my king valves was bleeding off refrigerant once the pressure got about 250 psi. I would check the valve and see if it bleeds once the pressure on your nitrogen bottle starts to get around 250 + just close the valve completely and see if it holds. If it does than it's definetley the valve.

  10. #36
    Join Date
    Sep 2002
    Posts
    13,544

    What is a buzz bulb ?

    What is a buzz bulb ?

    PHM
    -------

    Quote Originally Posted by meoberry View Post
    Yup! They do it. Had a lady customer that I went back to three times in a month. Ran entire system each time. No leaks. Recharged installed caps and marked caps on bottom. Sure enough Monday morning back out again. Caps had been moved. Noticed motion light right above unit. Found bulbs had been loosened. Told customer to run down to hardware store and pick up buzz bulb. Which I installed for her. She called following morning. She said it went off at 9:00 PM caught next door neighbor's kids with a bag and a piece of hose. Neighbor paid bill.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  11. #37
    Join Date
    Jun 2008
    Location
    NW Florida
    Posts
    713
    Quote Originally Posted by Poodle Head Mikey View Post
    What is a buzz bulb ?

    PHM
    -------
    It screws into a standard light socket and buzzes when you turn it on.

  12. #38
    Join Date
    Sep 2002
    Posts
    13,544

    What does a buzz bulb look like ?

    Is "buzz bulb" a standard term for this item?

    Does it look like a light bulb but makes a noise?

    How loud is the noise?

    I am sure that I have never seen or heard one. Or even Heard of one - before now.

    PHM
    -------




    Quote Originally Posted by meoberry View Post
    It screws into a standard light socket and buzzes when you turn it on.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  13. #39
    Join Date
    Jun 2008
    Location
    NW Florida
    Posts
    713
    Quote Originally Posted by Poodle Head Mikey View Post
    Is "buzz bulb" a standard term for this item?

    Does it look like a light bulb but makes a noise?

    How loud is the noise?

    I am sure that I have never seen or heard one. Or even Heard of one - before now.

    PHM
    -------
    I have not seen one in a few years. But it was shaped to fit in a light fixture with a speaker on the end. Last time I saw one was in Lowes. Check amazon.com.
    Last edited by meoberry; 07-31-2011 at 05:26 PM. Reason: more info

Page 3 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event