    I'm working on a service call that has been handled by someone else previously. I have a rheem RPMD042JAZ and for the past couple years the homeowner has said that freon has to be taken out every winter and added in summer. Any sugestions??? I'm thinking maybe TXV or some other metering problem or airflow. Just thought I would get some input before I go to the site. Thanks

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,590
    Proper indoor coil? Proper line sizing? First 2 things to check.

  3. #3
    rheem heat pumps must be matched with proper coil or air handler.

  4. #4
    Join Date
    Oct 2004
    Posts
    3,400
    And the ductwork has to be as specified in the installer's guide.

    (Same size as bonnet opening, tabs turned up, three feet with no start collars.)

    "Static Regain" is the fancy name.

  5. #5
    Could be that unit was overcharged in Spring and when called for heat in the Fall the high pressure limit was reached turning off the condensor...thus the need to remove refrigerant to get heatpump to operate properly. Assuming proper charge in Summer can't understand reason changing it in Winter.

    I believe that particular model (assuming that it is matched to the proper Rheem airhandler which includes a TXV)is more tolerant of overcharge conditions in the AC mode and less tolerant in the heatpump mode.


  6. #6
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Originally posted by bwal2
    And the ductwork has to be as specified in the installer's guide.

    (Same size as bonnet opening, tabs turned up, three feet with no start collars.)

    "Static Regain" is the fancy name.

    This is what we find as the cause of low airflow ,in all most all of the Rheem/Rudd installs, in are area.

    Most all still have a bright orange/red sticker on the top of the cabinet telling the installer what to do.It amazes me that so many are installed this way.

  7. #7
    Join Date
    Feb 2004
    Posts
    2,597
    according to our ruud rep, the static regain will no longer be necessary with the new series air handlers.

    the lack of the static collar is a common problem around here.

    your only choices are to keep adjusting the charge every fall and spring or correct it.

  8. #8
    Join Date
    Oct 2004
    Posts
    3,400
    Originally posted by billva
    according to our ruud rep, the static regain will no longer be necessary with the new series air handlers.
    That's good news.

  9. #9
    Join Date
    Oct 2003
    Posts
    2,866
    Found this same problem today. 13 seer rheem ht pump with a 10 seer evaporator coil. The coil had been changed 18 months ago Hi side pressure switch would trip out at 420 lb. i changed the coil to the recommended coil and had to actually add freon.
    I love my job.

  10. #10
    Join Date
    Oct 2003
    Location
    Florida's space coast
    Posts
    2,538
    I've been hearing about the new air handlers for about a year now but have yet to see one.

    Does anyone (doc) know when we can expect them and will there be much of a difference in height?
    We've been doing so much,for so long,with so little, that now we can do almost anything, with nothing at all.

  11. #11
    Join Date
    Feb 2004
    Posts
    2,597
    the higher seers are going to a 40-42" height, i believe the base 13 airhandler will remain the same.

  12. #12
    Join Date
    Apr 2004
    Posts
    7,680
    Yes, word is they will be taking orders shortly. I think it's fair to say they will be slightly taller but not much. (maybe 7").

    As far as the OP goes, you need to look at several things. First would be match. It has to be matched.
    Second, Airflow. If you are lacking airflow, you will overcharge it in cooling naturally. Which leaves you overcharged in heating. You need to know the actual airflow before you try to correct it. And yes, are the tabs bent up?
    Third, Line size and length. Is that correct? Being a 3.5 ton, I am not too concerned about the size but the length and vertical seperation (OD above or below?)
    Fourth. Dont go assuming the TXV is bad until you actually read superheat.
    Fifth, frost the coils, insided and out and look for a circuit that doesnt frost.
    Sixth, if all else is perfect, recover the refrigerant, triple evacuate, breaking with nitrogen, and weigh the charge in. (I did say triple evacuate, not just evacuate).


  13. #13
    Join Date
    Sep 2005
    Posts
    53
    oh yeah I've ran into the tabs not being bent up in a Rheem airhandler. It was installed in a attic space in the middle of july in Ga. none the less. Not a plesant experience to say the least. thanks for the help and ideas to go on. From what I've experienced here the charge on R22 esp. Rheems, isn't nearly as critical in the summer as it is in the winter. Thats as far as the unit cutting out on high press. of course. Either way it needs to be properly charged but the defrost cycle and other factors make it more crutial in the winter on heat pumps.
    I just don't see how some techs just add evac freoan from season to season and don't even try to eliminate the problem. They need to find something else to do for a living as far as I'm concerned.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event