07-24-2011, 08:16 PM #1
Heat exchanger
The system is closed loop with wshp and cooling tower.
Closed Loop
Entering Heat exchanger 108 F
Leaving Heat exchanger 103 F
Cooling tower
OAT 85 F
Entering Heat exchanger 82 F
Leaving Heat exchanger 94 F
What should the split on the heat exchanger be?
-
07-24-2011, 09:09 PM #2
Not that high.
The ones I have worked with have been zero to three degrees TD.
If it is a plate / frame or shell / tube it may need to be cleaned.
-
07-24-2011, 10:22 PM #3
Air in system
Thanks AiResearch
Would air in the closed loop cause this also?
Some wshp's have been replaced. The make up water most likely has gotten low.
-
07-24-2011, 10:41 PM #4
Absolutely! Air in the system can cause all sorts of good times.
And you are correct , most installers do not concern themselves with introduced air during a changeout.
There should be auto air bleeders at the highest point in the system , but those are un-reliable in my experience , you can :
- remove the air bleeders from the highest point , which is easy if there are shut off valves , you can do even if valves are not present b/c the water pressure is usually the lowest at that point , do it hot and install a ball valve , then check for air by opening the valve. when finished replace the bleeder.
- a better option is , if an air seperator is present , they are far quicker and more effective at removing air from the loop , a nice 1/2" ball valve on the top of that device will rid air in a heartbeat.
Check your makeup water , is it on? , is the regulator adjusted correctly? You will have to add water if you get much air out , if there is an expansion tank with a site glass , I remove air over and over and over at the serarator while throttling make up water at the same time , eventually you will see a bit of water in the site glass on the expansion tank. A good make up water system will have a regulator bypass , that makes the process faster.
Your system may not have these components or different versions , you may have to get creative , but a proper system should have these components in one variation or another.
Sorry for the jumbling on the info.
Your water level is most likely low , have any units been shutting off on HPS?
-
12-15-2012, 10:08 AM #5
Nice explanation Airreserch. Nice.
Sent from my SGH-T989 using Tapatalk 2