  1. #14
    Join Date
    Jun 2005
    Posts
    178
    no gas in the area so if i go with oil and use a direct vent i will go with the forced hot air because thats what he wants.hes been using oil for the past 10 years and he is stuck on it.he is also putting in a fire place so what ever is put in will not be used that much in the evening. canti over size the tripple wall chimney and use that for both the fire place and the furnace.

  2. #15
    Join Date
    Jan 2001
    Location
    Pacific Coast of Canada
    Posts
    4,008

    NO!!!!!

    You can not common vent a fireplace and a furnace in the same flue. No way, no how.
    As someone mentioned already, you can run a seperate A-vent chimney up the same wood framed chase as the fireplace chimney.

  3. #16
    Join Date
    Jun 2005
    Posts
    178
    yea i kinda knew that just wasnt sure im only a 4 year man

  4. #17
    Join Date
    Jun 2005
    Posts
    178
    ihavent done but maybe half dozen oil burners there any real demand for them anymore.

  5. #18
    Join Date
    Feb 2003
    Posts
    1,996
    While only 6% of the country heats with oil, about 50% of the N.E. still uses it. What about an oil fired package unit?

    http://www.thermopride.com/ThermoPack.cfm

  6. #19
    Join Date
    Oct 2005
    Posts
    923

    log cabin

    You really should do the two or even a three flue chimney. You have a basement for the clean outs and a log home deserves a wood / coal stove with forced air and thermostat controlled. You will wish you did it.

  7. #20
    Join Date
    Oct 2005
    Posts
    923

    log cabin

    I have a chubby wood coal forced air and it could warm the log home all day with about a 1/2 5 gallon buck of coal.

  8. #21
    Join Date
    Sep 2004
    Posts
    654

    Re: Complete Design and Selection

    Originally posted by dan sw fl
    Originally posted by coolcray3
    Im in N.J. ...
    helping my brother inlaw put up log cabin

    It is going to have AC also.
    The problem is that there is no natural gas to the area and
    we cant decide on direct vent oil burner or heat pump.
    H.P.!

    Electric $0.12/ kW
    $3.52 per Therm straight electric

    with C.O.P. 3.0
    $1.17 per Therm effective down to balance point (25-30'F).

    Oil $2.00/gallon ...
    90,000 BTUh IN x 90% Efficiency = 80,000 or 0.8 Therm
    =$2.50 Per therm

    Oil costs ~2X electric heat pump at >~25'F
    Electric Aux Heat at < 20'F will cost More.



    Oil provides 140,000 BTU per gallon, is that what was used in the numbers above? Doesn't appear so.

    A heat pump does not work well in Connecticut (for heating purposes that is), I suspect having a HP in NJ is not much better.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event