The motor will surely be replaced, but I'd like to know what might cause this for my own knowledge.
Thanks for all the replies!
-
07-24-2011, 03:37 PM #16[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
07-27-2011, 08:09 PM #17
Regular Guest
- Join Date
- Jul 2011
- Location
- Canton,Ma
- Posts
- 7
single phase will not run backwards only 3 phase can. if the rpm's look about right, correct the problem with a new fan blade thats meant for the rotation... a little cheaper than a new motor andless work. often most motors the rotation is if you were looking at the butt end of the motor unless it says cwse or ccse that woull be shaft end of the motor. I have run into motors spinning backward such as 9w motors in supermarket evaps, usually can be corrcted by clipping the capacitor wire (which is usually blue) and just having the 120 going to the motors.
-
07-27-2011, 08:38 PM #18
banned by Admin
- Join Date
- Jan 2011
- Posts
- 92
-
07-28-2011, 07:07 AM #19
Single phase motors are able to run in the opposite direction according to:
1) the position of a reversing plug
2) the condition of the windings and connections
3) the condition of the cap and the way the three (or four) wires are connected
In the case above, condition #2 is most likely. It would not be appropriate to install a fan blade for the "new" direction, since it is most likely that the current rotation is not what is on the label.
After checking connections, if the motor still turn the wrong way, replace the motor.[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES Certificate Member
AOP Forum Rules:
-
07-28-2011, 08:56 PM #20
Regular Guest
- Join Date
- Jul 2010
- Posts
- 15
I couldn't tell you exactly what happened inside your motor but it aint no good no more.
I have seen this alot on the Florida Heat Pumps in one building I work on they are 460 3 phase units that split out 2 legs and run a 460 split phase blower when these burn out they frquently run backwards. Chang the motor and move on.