    colonic for brazed plate

    Have a 10 ton thermalcare that is running about 15 degrees approach, any success stories on cleaning one?

  2. #2
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,888
    I would firstly call the mfg and see what they have to say.
    “It takes courage to grow up and turn out to be who you really are.”

    - E.E. Cummings

  3. #3
    Join Date
    Aug 2010
    Location
    Memphis
    Posts
    343
    Quote Originally Posted by chrishvacman View Post
    I would firstly call the mfg and see what they have to say.
    Maybe circulate acid through it but I would deffinatily check with manufacturer first

  4. #4
    Join Date
    Jun 2007
    Location
    Here. I'm right here i tell you!
    Posts
    465
    If its stainless do NOT use HCL!! The best I have seen to descale stainless is sulfamic acid. The chlorine in HCL will pit the metal. Check with a water treatment specialist and the MFG to confirm.