    help - Trane TWE 180 cannot get in cooling

    Please help - we have installed a 15 ton split system heat pump -- we are stuck in heating mode,, the reversing valve will not engage-- we have installed wiring per spec installation,,, is there something we are missing -- indoor fan is kicking but stuck in heatin mode.
    Thanks for any help

  2. #2
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    1,058

    It could be

    a number of things. Is this ReliaTel or standard controls? Do you have voltage to the RV solenoid?

  3. #3
    Yes it is a Reliatel and yes we do have 24 volt to solenoid - heating mode is still running even in cooling mode -- pulled leads of of reversing valve usually that will slide it over but it is still in heating

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,795
    Moved to Commercial forum.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5

    Greg Help

    Quote Originally Posted by gregp View Post
    a number of things. Is this ReliaTel or standard controls? Do you have voltage to the RV solenoid?
    Yes it is a Reliatel and yes we do have 24 volt to solenoid - heating mode is still running even in cooling mode -- pulled leads of of reversing valve usually that will slide it over but it is still in heating

  6. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,795
    dback. Don't make duplicate threads in the forums. I deleted your newest duplicate thread.

    If someone wants to and can help they will. if no one can, they making a bunch of post about this won't change that.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Jan 2006
    Location
    Near Atlanta, GA.
    Posts
    14,628
    Gentlemen,

    The new "Ask Our Pro" rules are in effect. Only a Pro Member with a * by their title may give advice.

    Advice posts by others may be deleted.

    Thanks

  8. #8
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    1,058

    If you

    are getting the proper voltage to the solenoid coil and it is not switching, you need to contact your Field Service Rep. Since this is a new unit, it may be a warranty issue for either a new solenoid or reversing valve. Before replacing any parts, I would contact the FSR and they can assist you step-by-step.

  9. #9
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    1,627
    As per the AOP Rules only Professional Members * can reply with advice to the OP. Anyone may post and ask questions. They may even question the * member answer but not give advice or expand on the advice given. Please read these rules for a complete understanding. AOP Rules

    For those in our industry who wish to become a Professional Member, please click here and follow the instructions. Apply for Professional Membership
    Last edited by Chris_Worthington; 07-22-2011 at 10:54 AM.
    Doug

  10. #10
    Join Date
    Dec 2003
    Location
    Citrus County, Florida
    Posts
    1,627
    Now that I have permission.... you have 2 separate units each 7 1/2 ton. Activate the other section (stage) AND SEE IF YOU HAVE COOLING. The chance that both RV's are bad are slim. If both sides won't cool, look at your controls.
    Doug

  11. #11
    Join Date
    Nov 2004
    Location
    Agawam, Ma
    Posts
    43
    Just my 2 cents, IF you are not the Global Moderator I or anyone else don't need you telling me the rules. That's what they are here for. If you want to be a rule enforcer then become a Global Moderator.

  12. #12
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,725
    Quote Originally Posted by k-fridge View Post
    Gentlemen,

    The new "Ask Our Pro" rules are in effect. Only a Pro Member with a * by their title may give advice.

    Advice posts by others may be deleted.

    Thanks
    Wow it must be really easy to get one of those how can I get 2* by my name?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  13. #13
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,725
    Quote Originally Posted by dback View Post
    Yes it is a Reliatel and yes we do have 24 volt to solenoid - heating mode is still running even in cooling mode -- pulled leads of of reversing valve usually that will slide it over but it is still in heating
    I bet your not reading your 24 volt correctly or maybe someone else un-wired the coils somewhere else. I smell wiring issues.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event