Page 4 of 4 FirstFirst 1234
Results 40 to 45 of 45
  1. #40
    Madison, WI/Cape Coral, FL
    [/B][/QUOTE]
    The RH setting depends on the quality of the windows and how cold it is outside. A good starting setpoint in the heating season is 35% when it is below freezing out and 50% when it is above freezing out.
    Will not be a sweaty window problem when ambient dewpoint is 45F with a ventilated home. Running on a timer could control humidity, running by a dehumidistat will minimize run time especially in the coldest weather.
    [/B][/QUOTE]
    The quality of the window and the indoor temperature are fixed. The outdoor temperature/dew point are a varible. The inside %RH/dew point must vary with outside temperture to avoid condensation. An outdoor temperature of 32^F may require 40%RH. A -10F outdoor temperature require <25%RH to avoid condensation. In other words, you must re-adjust the indoor %RH to match the changing outside condition. Otherwise the HRV will operate all the time during high outdoor dew points or none of the time during the low dew points.
    Combining the fresh air ventilation with time of occupancy is critical regardless of the potiential window problem. This leaves me with the opinion that a timer routinely providing the ventilation while the home is occupied with enough hours to remove the moisture from the occupants is simplest. The resulting inside dew point/%RH will vary with the outside dew point. This provides year around consitant ventilation. Just a difference of opinion. TB
  2. #41
    Apr 2002
    How about "the quality of the window is fixed and the indoor room temperature is fixed as long as the thermostat is not set back at night or while the occupants are at work . The outdoor temperature, dewpoint and the inside surface temperature of the glass are a variable."
    U-shaped condensation pattern is common in particular when there is not a good thermal break between the panes of glass. The indoor dewpoint and the inside temperature of the windows (which will be colder than the room air in the middle of the room) determines whether there will be condensation or not.
    Usually you get your coldest ambient temperatures as 'the overnight low' and combine this with the thermostat being setback at night and the windows can become significantly cooler. Bay windows are prone to being cooler cause the surrounding air loses heat compared to the rest of the room. Keeping the curtains closed lets the air between the window and glass cool, and the inside surface of glass gets cold and is more prone to sweating.
    Running the system on a fixed timer will probably control the condensation problem, but it could over dry or under dry the home as well. Why set it to time when you need to control RH?
    Running it when humidity rises will control condensation and operate only as much as required.
    Water vapour is a by product of respiration and so is CO2. If you neglect cooking or a housewife 'sweating to the oldies' humidity is being generated by people breathing. So in a lot of situations excluding hydroponic operations etc, it is possible that a ventialtion system responding to a rise in humidity is indirectly responding to a rise in CO2.
    Intermittent ventilation of a high enough rate can cycle on/off as the humidity builds up, better in my humble opinion, than drying the house bone dry for 12 hours straight, then letting it get rehumidified for 12 hours.
    You can use timers for minimum run times every hour, but why use time to control humidity? Control it with a dehumidistat.
    http://www.ductstrap.com/
  3. #42
    Apr 2002
    Good windows will allow 35% RH during some extreme weather.
  4. #43
    Cabot, PA
    Thanks for all the responses. All the points are quite valid and after hearing all of the arguments I think my soloution is going to be going with a dehumidistat. Iam going to have to do a little research on the proper way to do control wiring circut on the AprilAire unit that is being used but I think this is a good soloution to the problem at hand .If anyone else has done this kind of a hookup any suggestions would be greatly appricated.
  5. #44
    Apr 2002
    Teddy
    I see what you are getting at, but in the heating season, there is no outdoor dewpoint that is going to be detrimental.
    The humidity settings you mention , concerning dialing the setting up and down, remind me of those on the controls of residential humidifiers which are going extinct in new homes in Canada. People have been setting humidifiers up and down for years.
    With good windows, you can maintain 35% during some pretty cold weather. The homeowner will soon learn what level avoids condensation in the coldest weather.
    I was working on an automatic RH reset before I left Canada but back then it looked like I was re-inventing the wheel.
    From reading this site, it seems as though that some humidifier set points are being reset automatically with respect to outdoor temp, so it makes one wonder why you could not reverse the output of these controls with a relay or two.
  6. #45
    Apr 2002
    If the dehumidistat did not turn on the HRV during low ambient dewpoints, you would almost think the house was so drafty it would need a humidifier