    KALA-016E TAC 800

    Anyone know the capacity @ medium temp using R134a ?

  2. #2
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,152
    Quote Originally Posted by VTP99 View Post
    Anyone know the capacity @ medium temp using R134a ?
    Here's the capacity when used in a Copeland "C" line unit.

    10,230 btuh @ +20 SST @ 90 Ambient
    11,350 " " "

  3. #3
    Join Date
    Jan 2010
    Posts
    6,327
    Quote Originally Posted by powell View Post
    Here's the capacity when used in a Copeland "C" line unit.

    10,230 btuh @ +20 SST @ 90 Ambient
    11,350 " " "
    Thanks powell
    And what is the "C" line ?
    This compressor is runinng 3 Russel evaporators in a floral display.
    Russel model # WE 18-55
    5500 btur @ 10* TD
    6600 btur @ 12* TD
    3-front glass doors & 1-end glass door.
    What's your thinking ?
    Thanks,
    VTP

  4. #4
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,152
    Quote Originally Posted by VTP99 View Post
    Thanks powell
    And what is the "C" line ?
    Sorry for the tardy response, I had to wait for my AOP clearance.

    The C-line is/was a popular Copeland unit that I've used for years to establish the approximate buth's of a semi-hermetic compressor. You'd recognize them, they have two horizontal receivers mounted under the compressor and they're built like a tank.

    Quote Originally Posted by VTP99 View Post
    This compressor is runinng 3 Russel evaporators in a floral display.
    Russel model # WE 18-55
    5500 btur @ 10* TD
    6600 btur @ 12* TD
    3-front glass doors & 1-end glass door.
    What's your thinking ?
    Thanks,
    VTP
    The unit and evaps are matched good. It equates to about a 7.6 TD for a 38 degree box. That's good for maintaining the required higher humidity in a floral box.

    Without knowing the box dimensions I can't speak for the btuh capacity required.

  5. #5
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,379
    The "c" line is commonly referred to as a "pontoon unit". Like the boat. Its good for selling ots of refrigerant.

  6. #6
    Join Date
    Jan 2010
    Posts
    6,327
    I here ya Joe
    When i walk up to those type of units my jug starts to scream
    Last edited by VTP99; 07-23-2011 at 09:40 PM.

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,375
    Somebody at Copeland was on the ball when they designed that unit oh so many years ago.

    Those twin receivers made for excellent structural rigidity and allowed for a lower profile.

    Also, because the receiver diameters were typically under 6", they didn't have to ASME Certified and inspected vessels....which equated to a boatload of cost savings.

    Best of all, that parallel design actually worked.

  8. #8
    Join Date
    Jan 2010
    Posts
    6,327
    Quote Originally Posted by powell View Post
    Sorry for the tardy response, I had to wait for my AOP clearance.

    The C-line is/was a popular Copeland unit that I've used for years to establish the approximate buth's of a semi-hermetic compressor. You'd recognize them, they have two horizontal receivers mounted under the compressor and they're built like a tank.


    The unit and evaps are matched good. It equates to about a 7.6 TD for a 38 degree box. That's good for maintaining the required higher humidity in a floral box.

    Without knowing the box dimensions I can't speak for the btuh capacity required.
    Thanks again powell.
    They are not using the box for flowers so the TD is not so important.
    Form what i'm told the last coil has a tendacy to freeze.
    Those coils have a total capacity of 1.5 ton and your saying that compressor is less then a ton. So i'm worried about that.
    I'll get the box size for you to see what you think.
    Thanks,
    VTP

  9. #9
    Join Date
    Jan 2010
    Posts
    6,327
    Quote Originally Posted by icemeister View Post
    Somebody at Copeland was on the ball when they designed that unit oh so many years ago.

    Those twin receivers made for excellent structural rigidity and allowed for a lower profile.

    Also, because the receiver diameters were typically under 6", they didn't have to ASME Certified and inspected vessels....which equated to a boatload of cost savings.

    Best of all, that parallel design actually worked.
    icemeister,
    These condensers sure hold a large charge.
    Do you think that was for long run remote setups ?

  10. #10
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,006
    I service a LAC-3 3 hp Low temp with the dual receivers underneath. A lot of refrigerant!!!!
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  11. #11
    Join Date
    Sep 2006
    Location
    Chicago
    Posts
    474
    Name:  IMAG0083.jpg
Views: 167
Size:  41.1 KB

    "The pontoon"

  12. #12
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,375
    Quote Originally Posted by VTP99 View Post
    icemeister,
    These condensers sure hold a large charge.
    Do you think that was for long run remote setups ?
    Large receivers were pretty much the standard years ago. Those were the days when quality and suitability for an application really meant something.

    When I started out, most supermarkets were still conventional, single compressor systems. It was typical for a 3 HP unit to have at least a 40 lb receiver, a 5 Hp might have a 60 and a 7 1/2 could have a 100 lb or larger.

    Today, it's tough to find a stock unit with anything close to that kind of pumpdown capacity...except for the C-Line Copeland.

  13. #13
    Join Date
    Jan 2010
    Posts
    6,327
    Quote Originally Posted by icemeister View Post
    Large receivers were pretty much the standard years ago. Those were the days when quality and suitability for an application really meant something.

    When I started out, most supermarkets were still conventional, single compressor systems. It was typical for a 3 HP unit to have at least a 40 lb receiver, a 5 Hp might have a 60 and a 7 1/2 could have a 100 lb or larger.

    Today, it's tough to find a stock unit with anything close to that kind of pumpdown capacity...except for the C-Line Copeland.
    icemeister,
    Do you know of a way to figure the capacity on these receivers ?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event