Results 1 to 9 of 9

Thread: carrier chiller

  1. #1
    Join Date
    Aug 2010
    Location
    Buckeye,AZ
    Posts
    2
    Post Likes

    carrier chiller

    any body know what a 19FA chiller sounds like when it phase rotation is wrong?

  2. #2
    Join Date
    Oct 2004
    Location
    Texas
    Posts
    1,176
    Post Likes
    UH not good??
    Saddle Up!

  3. #3
    Join Date
    Dec 2008
    Location
    Dixiana, AL
    Posts
    2,625
    Post Likes
    Some centrifugals won't run (long) in reverse rotation. Others will do a surprising amount of tonnage when running backwards. I've had the pleasure of diagnosing a handful of machines that were placed into operation in reverse and left that way, one of them for several years. That one in particular did 6.5* out of a rated 10* delta T when running with the vanes wide open at rated FLA (or as close as it would get). It also had some SERIOUS discharge superheat going. As far as unusual noise, they've all sounded somewhat odd, but not enough so that I would have said that there was a problem in the compressor just because of the sound. That said, I've never had an FA with that problem, so I can't say specifically, just generally.

  4. #4
    Join Date
    Feb 2004
    Location
    Northwest GA
    Posts
    602
    Post Likes
    If it's a 19 FA you should be able to check rotation on spin down through the S/G at the end of the motor. Or use the S/G on top of the gear case.
    Superheat, that must be REALLY hot.

  5. #5
    Join Date
    Mar 2007
    Posts
    3,632
    Post Likes
    If the rotation is wrong, it'll make a noise like "WEEEEEEEEEEEE..."
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  6. #6
    Join Date
    Mar 2007
    Posts
    3,632
    Post Likes
    If he were asking about a 17FA, I would be worried.
    The key to happiness is lower expectations.

    Don't pick the fly crap out of the pepper.

  7. #7
    Join Date
    Jul 2001
    Location
    maryland
    Posts
    1,398
    Post Likes
    phase meters are cheap.
    Saving the world...one service call at a time.

  8. #8
    Join Date
    Feb 2007
    Location
    Baltimore MD ( Balimer, Murilyn)
    Posts
    148
    Post Likes
    There's a sightglass on the motor shell. Look in the glass when the motor is STARTING. Rotation is clockwise.

  9. #9
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,201
    Post Likes
    isnt there a phase monitor on the machine??
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.