Results 1 to 9 of 9
Thread: carrier chiller
    Aug 2010
    Buckeye,AZ
    carrier chiller
    any body know what a 19FA chiller sounds like when it phase rotation is wrong?
    UH not good??
    Saddle Up!
    Dec 2008
    Dixiana, AL
    Some centrifugals won't run (long) in reverse rotation. Others will do a surprising amount of tonnage when running backwards. I've had the pleasure of diagnosing a handful of machines that were placed into operation in reverse and left that way, one of them for several years. That one in particular did 6.5* out of a rated 10* delta T when running with the vanes wide open at rated FLA (or as close as it would get). It also had some SERIOUS discharge superheat going. As far as unusual noise, they've all sounded somewhat odd, but not enough so that I would have said that there was a problem in the compressor just because of the sound. That said, I've never had an FA with that problem, so I can't say specifically, just generally.
    Northwest GA
    If it's a 19 FA you should be able to check rotation on spin down through the S/G at the end of the motor. Or use the S/G on top of the gear case.
    Superheat, that must be REALLY hot.
    If the rotation is wrong, it'll make a noise like "WEEEEEEEEEEEE..."
    The key to happiness is lower expectations.
    Don't pick the fly crap out of the pepper.
    If he were asking about a 17FA, I would be worried.
    Jul 2001
    maryland
    phase meters are cheap.
    Saving the world...one service call at a time.
    Feb 2007
    Baltimore MD ( Balimer, Murilyn)
    There's a sightglass on the motor shell. Look in the glass when the motor is STARTING. Rotation is clockwise.
    Not in Iran
    isnt there a phase monitor on the machine??
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
