    Post Likes


    customer called about above furnace.would not come install by another contractor. air worked in summer,but no heat at start of season.found fuse blown on board.found t-wire was pinched where it passed through the ceiling to apartment t-stat.replaced wire and ran for a customer says fuse is blown again.I don't work much on fridgidare there something I should be looking for,other than overt one. model fg6rk 096c-16b thanks taunch

  2. #2
    Join Date
    Mar 2004
    SE Michigan
    Post Likes
    You have a short on the 24 vac side. Get out your meter and track it down.