Thread: fridgidare furnace
-
10-26-2005, 04:16 AM #1
Regular Guest
- Join Date
- Oct 2002
- Location
- chicago
- Posts
- 3
customer called about above furnace.would not come on.new install by another contractor. air worked in summer,but no heat at start of season.found fuse blown on board.found t-wire was pinched where it passed through the ceiling to apartment t-stat.replaced wire and t-stat.it ran for a week.now customer says fuse is blown again.I don't work much on fridgidare units.is there something I should be looking for,other than overt one. model fg6rk 096c-16b thanks taunch
-
10-26-2005, 07:48 AM #2
You have a short on the 24 vac side. Get out your meter and track it down.
"If anybody can draw on the power, where do we put the meter?" - JP Morgan before pulling Tesla funding


Reply With Quote