R409a vs R134a
Went to take a look at a reach in cooler. I believe it was a Randell made in 1985. The unit was cutting out on overload. The tech before me replaced the compressor. Any way the inside temperature was around 60 degrres. I hooked up my gauges and got pressures of 30/200. The unit was in a kitchen and the ambient was 103 degrees. I know with that low suction pressure and high SH, I had a restriction. I guessed that the refrigerant used was R409a because when I shut the unit off the pressure settled down to 150-155 on the liquid side. The suction did not get much higher than 50psi. I think that the subcooling was around 9-10 degrees. Anyway I was wondering if there is any reason they stuck with R409a when they replaced the compressor rather than go with R134a?
Stuart
Lack of airflow destroys compressors.
-
07-18-2011, 08:24 AM #2
New Guest
- Join Date
- Oct 2010
- Posts
- 5
I think R134a is much more common for refrigeration system and heat pumps.
-
07-18-2011, 03:40 PM #3
Regular Guest
- Join Date
- May 2010
- Location
- fallbrook
- Posts
- 16
it depends on the compressor, was it an r12 or r134a compressor. I would only use r134a for an r134a compressor. If it was r12 compressor than thats why they used r409a. R409a is a blend for r12. My preference is hot shot but it really depends on the tech and what they like to use.
-
07-18-2011, 04:25 PM #4
Did you look at the expansion vlv to see what kind of gas or run the compressor numbers by the supply house to see what it is? R409a you can drop right in an R12 rated system with out major changes. I have also added R409a on top of R12 with no major issues.
Not what it use to be
-
07-18-2011, 09:23 PM #5
Professional Member*
- Join Date
- Apr 2003
- Location
- Maple Grove, MN
- Posts
- 713
Why do you think 30psi suction pressure is too low for a r-12 type system? Also, just because r-134a is more common, it doesn't mean it is a better refrigerant. For a small system that started out with r-12, r134a would be my LAST choice as a replacement. This is because the POE oil that is required with r134a is a horrible lubricant when used in the real world. It breaks down and turns to crap that will plug your cap tube if it ever over heats or has any bit of moisture in it.
-
07-23-2011, 09:18 AM #6
Professional Member*
- Join Date
- Apr 2004
- Location
- Des Plaines,IL
- Posts
- 956
-
07-23-2011, 09:21 AM #7
Professional Member*
- Join Date
- Apr 2004
- Location
- Des Plaines,IL
- Posts
- 956
Stuart
Lack of airflow destroys compressors.
-
07-23-2011, 09:25 AM #8
Professional Member
- Join Date
- Apr 2005
- Location
- Central California
- Posts
- 185
-
07-23-2011, 09:27 AM #9
Professional Member
- Join Date
- Apr 2005
- Location
- Central California
- Posts
- 185
Is this a captube?
Only Chuck Norris can slam a revolving door
-
07-23-2011, 10:20 AM #10
Professional Member*
- Join Date
- Apr 2004
- Location
- Des Plaines,IL
- Posts
- 956
-
07-23-2011, 01:10 PM #11
These reach-in units are designed for an ambient of 80f. At an ambient of 103 all the reach-ins are getting killed.