Thread: Insulate box around Attic furnace

  1. #1
    Join Date
    Mar 2004
    Location
    New Hampshire
    Posts
    10
    Post Likes
    Unfortunately, my house furnace is located in the attic. I leave in NH so in the winter time it gets pretty cold up here. Researching the web, I found some opinions that folks say "consider building a large insulated box around the entire furnace--leaving an opening at the bottom for combustion air intake. Doing these two things would dramatically reduce the amount of warm air getting into the attic from the furnace source".

    What do you think about doing this?

  2. #2
    Join Date
    Feb 2003
    Posts
    1,994
    Post Likes
    I've heard this said when trying to put a 90% efficent furnace in an attic to prevent condensation freezing. But if the furnace doesn't draw air from a seperate combustion supply pipe, I don't see how boxing an 80% eff furnace in uncondition space would help. As soon as you allow cold air access to the furnace, you know the cold will migrate into the heat exchanger. Ductwork has more exposure in an attic. SO it must be well insulated.

  3. #3
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    ductwork includes the plennum where the supply ducts leave from, return piping & plennum (boxes at ends of air handler0
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  4. #4
    Join Date
    Sep 2005
    Posts
    12
    Post Likes
    I have applied for an energy star rating on our new house in NH. This was one of their recommendations:

    Suggest that the HVAC air handler in the attic be enclosed in a well insulated equipment room (R-19 or greater) - and - ALL the ductwork in the attic should be insulated to R-19 or greater ( Not R-4.3 ). It is more costly to have your conditioned space heating/cooling air running through a poorly insulated HVAC system in the cold/hot attic.

  5. #5
    Join Date
    Jul 2004
    Posts
    322
    Post Likes
    I'm sure setups vary, but my furnace is fairly well insulated with foil faced insulation that seems to work well by the crude measure of feeling the outside of the box when the furnace is running. The air handler, on the other hand, is poorly insulated, with no insulation at all on the removable door in front.

  6. #6
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    Building a box sounds like a small box covering the furnace, a framed and insulated mechanical room sounds much more attractive. Just make sure to have adequit combustion air and room for the technician to operate.

  7. #7
    Join Date
    Sep 2004
    Posts
    3,157
    Post Likes
    building a box is a great suggestion for the guy selling boxes, you would need a hole for combustion air....a big hole ....a hole big enough to let in the same cold air .

    a box wont keep your furnace warmer

  8. #8
    Join Date
    Feb 2003
    Posts
    1,994
    Post Likes
    For an energy star rated home don't you need a 90% furnace installed? That might be the reason for an insulated room to prevent condensate freezing.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •