Results 1 to 8 of 8
Thread: Charging a Heat Pump
-
10-23-2005, 09:09 PM #1
Professional Member
- Join Date
- Oct 2005
- Posts
- 96
If a contractor is charging a heat pump in 40 degree weather is it true that he cannot get a sufficient charge on it to meet my summer high temp conditions? I know this was the case in the old compressors but wasn't sure if this was still the case. If I have a contractor install a heat pump in this weather do I need to have him come back and check the refrigerant charge when the temperature warms up?
-
10-23-2005, 09:12 PM #2
No, he can weigh it in. In other words he can calculate the amount of refrigerant needed and charge the system by the required weight.
-
10-23-2005, 09:15 PM #3
Professional Member
- Join Date
- Oct 2005
- Posts
- 96
Is this true with either R-410 or R-22? I assume it doesn't matter? When you say weigh it in what does that mean?
-
10-23-2005, 09:36 PM #4
Use a scale, calculate the requried oz.'s needed for system and open valve. Shut valve off when scale reaches required number.
Karst means cave. So, I search for caves.
-
10-24-2005, 10:23 AM #5
Really, it depends on the unit, some units allow charging at lower temps. You really need to consult the unit charging procedures (which only apply to a properly installed system).
-
10-24-2005, 12:31 PM #6
Yes you can weigh in a charge in cool weather, but you should always have it checked during a hot day for proper charge. The weight a manufacturor specs is for up to "15-25ft" lineset, so charge can be off a little with the weigh in method. Always best to use subcool/superheat per manu's specs in cool mode IMO.
If everything was always done "by the book"....the book would never change.
-
10-24-2005, 07:42 PM #7
Heat pumps can also be adequetly charged in cold weather using the hot gas discharge method. It is a bit of a pain, but quite accurate.
Government is a disease......masquerading as its own cureEcclesiastes 10:2 NIV
-
10-24-2005, 11:54 PM #8
Professional Member
- Join Date
- Sep 2004
- Posts
- 284
Never even heard of such a method. Please enlighten me sir.Originally posted by RoBoTeq
Heat pumps can also be adequetly charged in cold weather using the hot gas discharge method. It is a bit of a pain, but quite accurate.


Reply With Quote