    w/i

    hi guys i have a celment w/i box i got there found temp @51f gas mp 39 water cool head was225psi back 27 i adjusted water reg to 175 had to water reg valve because it was laeking thru recoved freon charge drier recharge with 134 water temp going in 67 out 77 temp 43 box size 14x7x9 ht will be checking tomorrow have to get temp to 40 thanks phil

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    SUPERHEAT!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!???????? ?????????????!!!!!!!!!!!!!!!!!!!!!!!!!!!!????????? ?????????????!!!!!!!!!!!!!!!!!!!!!!!?????????????? ????

  3. #3
    Join Date
    Apr 2005
    Location
    Central California
    Posts
    186
    Post Likes
    You changed to 134 from mp 39...... Did you change oil also?

    Unless you already have ester oil in it
    Only Chuck Norris can slam a revolving door

  4. #4
    Join Date
    Apr 2005
    Location
    Central California
    Posts
    186
    Post Likes
    Quote Originally Posted by Phase Loss View Post
    SUPERHEAT!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!???????? ?????????????!!!!!!!!!!!!!!!!!!!!!!!!!!!!????????? ?????????????!!!!!!!!!!!!!!!!!!!!!!!?????????????? ????
    Haha are you tired of asking that question?
    Only Chuck Norris can slam a revolving door

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    27 pounds suction is pushing 30 degrees evap.


    Going to have a hard time maintaining a cold box that way.

    Head pressure seems a shade high to me, too, but I didn't look it up.



  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by mr kev View Post
    Haha are you tired of asking that question?
    Superheat isn't important or anything.......



  7. #7
    Join Date
    Apr 2005
    Location
    Central California
    Posts
    186
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Superheat isn't important or anything.......
    Nah who needs it!?


    Besides the compressor of course
    Only Chuck Norris can slam a revolving door

  8. #8
    Join Date
    May 2011
    Location
    Spring City, Pennsylvania, United States
    Posts
    230
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Superheat isn't important or anything.......
    why would he ask about superheat? hes trying to make it cold...

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by ruuufuhbock View Post
    why would he ask about superheat? hes trying to make it cold...
    My point exactly......


    Probably needs more freeze-on



  10. #10
    Join Date
    Apr 2005
    Location
    Central California
    Posts
    186
    Post Likes

    Talking

    Quote Originally Posted by jpsmith1cm View Post
    My point exactly......


    Probably needs more freeze-on
    Thats the answer for everything

    When my customers call I always hear

    " my walk in is warm.....I think it just needs FREON"


    I also hate the term FREON. Maybe I am just being picky. When my guys say it I always correct them and say "refrigerant". Freon is just a brand by good ol dupont. Had to vent cause I remember this topic came up at work this past week
    Only Chuck Norris can slam a revolving door

  11. #11
    Join Date
    May 2011
    Location
    Spring City, Pennsylvania, United States
    Posts
    230
    Post Likes
    Quote Originally Posted by mr kev View Post
    Thats the answer for everything

    When my customers call I always hear

    " my walk in is warm.....I think it just needs FREON"


    I also hate the term FREON. Maybe I am just being picky. When my guys say it I always correct them and say "refrigerant". Freon is just a brand by good ol dupont. Had to vent cause I remember this topic came up at work this past week
    when i get a call like that i tell them to hold the phone up to the unit and then proceed to tell them can't fix it they need a new one!

  12. #12
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Quote Originally Posted by mr kev View Post
    You changed to 134 from mp 39...... Did you change oil also?
    first darn thing to pop in my head ... im not a 134a fan lol so that be the last thing id be looking to put it lol

  13. #13
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    OK Phil we need a lot more information:

    Mod # of compressor, Sr # would help also

    Superheat at evap and comp is needed.

    Evap and x-valve #’S

    If you give us the #’s we need then maybe you’ll get the information you need.

  14. #14
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Is there not a rule requiring punctuation on this site? Because just reading the original post makes me feel dizzy.

    One of my co-workers speaks so fast like he's in a super hurry, and I can hardly ever understand anything he's asking me. It reminds me of reading a post that has no punctuation.

  15. #15
    Join Date
    Dec 2008
    Location
    Nor•Cal
    Posts
    250
    Post Likes
    It shouldn't be so much work to understand your question. If you want our help, please take the effort to present your data in a clear manner. There are some really smart people on here and they are more than happy to help, but don't make it such a chore.

  16. #16
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    Quote Originally Posted by ruuufuhbock View Post
    why would he ask about superheat? hes trying to make it cold...
    Ahhhhhhh, it all makes sense now.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  17. #17
    Join Date
    Oct 2004
    Location
    Yakima, WA
    Posts
    1,847
    Post Likes
    Quote Originally Posted by mr kev View Post
    I also hate the term FREON. Maybe I am just being picky. When my guys say it I always correct them and say "refrigerant". Freon is just a brand by good ol dupont. Had to vent cause I remember this topic came up at work this past week
    Refrigerant is way too general of a term - that could be anything from water to ammonia. I insist people specify and call it chlorodifluoromethane, or difluoromethane-pentafluoroethane blend to keep from confusing the customer.

    Then I drink a coke(R) and blow my nose with a kleenex(R). I'll sometimes use another kleenex(R) to wipe down my channel-locks(R) and crescent(R) wrenches that were made by Craftsman(?).

  18. #18
    Join Date
    Apr 2005
    Location
    Central California
    Posts
    186
    Post Likes
    Quote Originally Posted by cjpwalker View Post
    Refrigerant is way too general of a term - that could be anything from water to ammonia. I insist people specify and call it chlorodifluoromethane, or difluoromethane-pentafluoroethane blend to keep from confusing the customer.

    Then I drink a coke(R) and blow my nose with a kleenex(R). I'll sometimes use another kleenex(R) to wipe down my channel-locks(R) and crescent(R) wrenches that were made by Craftsman(?).
    What's your definition of freon there cliff?

    Btw coke is bad for you
    Only Chuck Norris can slam a revolving door

  19. #19
    Join Date
    Apr 2004
    Posts
    6
    Post Likes
    Thread Starter

    Confused

    Quote Originally Posted by tazg View Post
    hi guys i have a celment w/i box i got there found temp @51f gas mp 39 water cool head was225psi back 27 i adjusted water reg to 175 had to water reg valve because it was laeking thru recoved freon charge drier recharge with 134 water temp going in 67 out 77 temp 43 box size 14x7x9 ht will be checking tomorrow have to get temp to 40 thanks phil
    compressor m#aha7480axd heatcaft evep adt090aj s/g fullhttp://hvac-talk.com/vbb/images/icons/icon17.gif

  20. #20
    Join Date
    Nov 2003
    Posts
    1,867
    Post Likes
    Quote Originally Posted by cjpwalker View Post
    Refrigerant is way too general of a term - that could be anything from water to ammonia. I insist people specify and call it chlorodifluoromethane, or difluoromethane-pentafluoroethane blend to keep from confusing the customer.

    Then I drink a coke(R) and blow my nose with a kleenex(R). I'll sometimes use another kleenex(R) to wipe down my channel-locks(R) and crescent(R) wrenches that were made by Craftsman(?).
    Can you Xerox® me a copy of this?

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •