Thread: crazy pressures
    May 2010
    New jeresey
    crazy pressures
    Guys checked charge which is correct.This is a 22 system 25 oz compressor at rated amps of 7 but compressor very ot suction is low 40lb head 200. I know there isnt enough to cool compressor. do you think suction valve bad.
    Jun 2011
    Rochester, NY
    How do the guys know the charge is correct with those pressures. What's the inside and outside temp and how old is the system. What seer. Txv or orifice. Whats superheat and subcooling. Are filters and both coils clean?
    May 2010
    New jeresey
    Charge removed and put back as per label ... water cooled.. 85 in 97 out.. filters clean... super heat 12 degrees .. also strainer clean. this is a heat pump unit.orifice metering device......
    Doesnt sound like a bad compressor to me.
    A bad compressor would tend to have a high suction, not a low suction.
    As a side note, it isn't smart to insult those who are trying to help you.
    May 2010
    New jeresey
    Confused
    sorry wasnt thinking I apologize having bad day.....
    More detailed system readings would tell a lot more about the problem.
    I've got a few ideas, but without a full set of readings, it isn't possible to guess.