Thread: Flame sensor micro amps

  1. #1
    Join Date
    Jun 2003
    Location
    Battle Creek MI Occupation: Simi-retired 57 year old, in home and shop appliance tecnician, (since 1967).
    Posts
    62
    Post Likes

    Hmm

    Lennox G2003E-75-2. Has spark-to-pilot module and seprate sensor rod. It has a pretty blue pilot with good impingement, I cleaned the sensor rod with a soft brass brush and clean white paper, my Fluke reads 1.4 micro amps in series with the sensor. The main valve wont kick in and the furnace goes into lockout. What micro amp reading should I be getting? (I think I have a weak module.) Thanks guys, from a 'retired' tech with a bad memory.

  2. #2
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    your reading seems ok

  3. #3
    Join Date
    Apr 2004
    Posts
    7,680
    Post Likes
    so what is the voltage from the sensor to ground?

  4. #4
    Join Date
    Apr 2005
    Posts
    517
    Post Likes
    Check for voltage at the main gas valve terminals or at the module output serving the gas valve. If your microamps are good your module should energize the gas valve main valve.

  5. #5
    Join Date
    Nov 2000
    Location
    Waco, Texas, USA
    Posts
    6,153
    Post Likes
    Try reversing the polarity. Your 1.4ľA reading should go up to 2.8ľA
    "And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.

  6. #6
    Join Date
    Jun 2003
    Location
    Battle Creek MI Occupation: Simi-retired 57 year old, in home and shop appliance tecnician, (since 1967).
    Posts
    62
    Post Likes
    Thread Starter
    I'm going back tomorrow, this furnace has worked fine 'till this season. Did you mean to check the polarity of the 120vac that powers the furnace? I will do that before replacing anything, however I do need to check for 24vac at the gas valve and continuity of the main coil on that valve also. The spark that lights the pilot keeps clicking untill lockout. I do expect voltage from the sensor to ground, but then again I don't remember what that reading should be. I do remember on some HSI units that if you get 103 to 105v from the sensor to ground, then the module is bad. Is it the same for spark to pilot? Thanks again guys.

  7. #7
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    Originally posted by wishful
    The spark that lights the pilot keeps clicking untill lockout.
    Here's your sign!




    I'm kidding BTW.

  8. #8
    Join Date
    Jan 2003
    Posts
    959
    Post Likes

    pv to mv

    make sure all you limits are good..

    roll out switch, high limit, provent switch, etc, all these could hold it back. What model of controler would help.

    When u get a pilot jump pv to mv. This will verify you have a good gas valve.

    regadrs,
    kelvin

  9. #9
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    ake sure the connection for the flame senser to the control is good and tight. i have seen a lot with loose spade connections and the true signal never reaches the control. i have also seen cases where the clip that holds the senser in place is loose and the senser drops down a little and dose not get the right recifacation.
    personaly i think you have a defective control. but just a guess

  10. #10
    Join Date
    Mar 2004
    Location
    Gone
    Posts
    5,340
    Post Likes
    Why don’t you idiots just give your phone numbers out so you can give every homeowner in the country step by step free advice so no contractor in the country can make a living.

    All you idiots are doing is building a file where every homeowner can go hit search and solve their problems here instead of calling a local contractor.

    What the heck do you think the Pro technical forum is for? Did you ever possibly think it might be to discuss matters such as this?

  11. #11
    Join Date
    Nov 2001
    Location
    chicago
    Posts
    101
    Post Likes
    Hey made in the usa good point, i hope they listen to you.

  12. #12
    Join Date
    Nov 2000
    Location
    Waco, Texas, USA
    Posts
    6,153
    Post Likes
    Yeah I agree. By the lingo he was using he sounded competent but after reviewing his past posts I now realize he is an illegal side jobber being very selfish in taking work away from legitimate contractors. Sorry wishful, no more technical help.
    "And remember my sentimental friend......that a heart is not judged by how much you love, but by how much you are loved by others" - Wizard of Oz.

  13. #13
    Join Date
    Oct 2005
    Location
    Canada
    Posts
    256
    Post Likes
    One must keep an open mind.
    it could be an "impossible" to clean impregnated sensor rod even another malady of same.
    OR could be 'nother issue entirely.

  14. #14
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,881
    Post Likes
    early model g20 has the blues prolem

  15. #15
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,086
    Post Likes
    Originally posted by madeinusa
    Why don’t you idiots just give your phone numbers out so you can give every homeowner in the country step by step free advice so no contractor in the country can make a living.

    All you idiots are doing is building a file where every homeowner can go hit search and solve their problems here instead of calling a local contractor.

    What the heck do you think the Pro technical forum is for? Did you ever possibly think it might be to discuss matters such as this?
    Since everyone can get into the pro section what is the difference?

    This type of thread is what catches my attention. This is the tread that we can teach each other. Some tech will read this thread and remember that older G20s had an issue with the original control module. Now a few HO's will also. Bitter medicine.


    As far if Wishful needs to be helped, not my call. I spend too much time here as it is, and don't need to be policing this site.

    Beware of advice given by some guy on the Internet.

  16. #16
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    check the heatexchanger while you are there. the G-20 had problems with deteorating hx. seemed to me it was the hx that was painted that had most of the trouble. lenox later changed it to a nonpainted one and seemed to solve the problem.

  17. #17
    Join Date
    Jun 2003
    Location
    Battle Creek MI Occupation: Simi-retired 57 year old, in home and shop appliance tecnician, (since 1967).
    Posts
    62
    Post Likes
    Thread Starter

    Exclamation

    Hey folks, I didn't mean to tic anybody off. I have deals with contracttors in this area to help out when they are overburdened or shorthanded. Since I got cancer I can no longer work full time. But a lot of days I feel good enough to be useful, and with some of the young guys needing more experience we can all work together. On that note, I found my tech manual for the Lennox in question, and the furnace will either be fixed right or condemned. By the way-- do you think the average HO would know what flame rectification is, or microamps for that matter.
    I was just using this forum to jog my memory. If you do your jobs well & charge a fair price, then you have nothing to worry about.
    Thanks again to the good folks with the helpful attitudes.

  18. #18
    Join Date
    Mar 2005
    Posts
    661
    Post Likes
    Steve Wiggins
    Professional Member

    Registered: Nov 2000
    Posts: 4667
    Try reversing the polarity. Your 1.4ľA reading should go up to 2.8ľA
    __________________


    Steve how do you figure that? If you reverse the polarity on a DC ampmeter you should get -1.4uA. Or are you just trying to be cute? The only time I have seen what you said was when my multimeter went flakey.

    Sounds to me like the pilot orifice is pluged up. Try replacing it. We seem to have a lot of problems with them on propane especially in damp basements and Roof Top Units. By the way you should have around 3 to 5 uA of flame current.

    [Edited by lakeman1234 on 10-24-2005 at 12:42 AM]

  19. #19
    Join Date
    Mar 2004
    Posts
    20
    Post Likes
    Don't worry too much madeinusa.
    Most homeowners don,t have the proper tools to do the trouble-shooting, much less what to even look for.Just take a look the money you've invested in your equipment to do what you do.Years ago I owned a tire & auto repair business.Busted my --- 15years trying to keep up with Sears,PepBoys,Sams,...etc.When I soldout I had over 50K in equipment and trucks air-compressors,balancers...you name it.Now when I have a flat or a tire out of balance I have to go to someone who's in the tire buisness.Even though I know how to do it..I don't have the equipment to do it.I remember when I worked for a restaurant chain just about every gas fired appliance they had used RobertShaw valves. At the time i could tell you anything you needed to know,but now I'm trying to keep up with the rapidly changing HVAC technology I can't remember that old stuff anymore.I didn't use it,so I loosed it.What's killing me is all these shoddy cut-throat competitors.It's hard to turn a buck anywhere. I can't have the whole pie but I can sure have my piece.Just find your niche and keep a bead on it.Don't be afraid to tell someone what you know, thats how we learned what we know...All of us had to learn at one time too. I visit this site to laugh and LEARN...it's FUN! I've had some Vets on this site save my butt a lot of times just because they wanted to and I really appreciate them.By the time you know alot it's time to die.Don't let all that experience and knowledge go quitely into the night, tell me what you know and your eyes have seen , WE NEED YOU!

  20. #20
    Join Date
    Apr 2004
    Location
    Bass Lake, IN
    Posts
    6,629
    Post Likes
    I don't know what kind of advice you guys are giving this poor guy, but you're gonna get him hurt, it's obvious the problem lies in the time delay in the ODFM this is the first thing you want to check before goin through all that other trouble.

    Good luck

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •