Thread: Variable speed vs multi-speed blowers

  1. #1
    Join Date
    Oct 2005
    Location
    Hockessin,DE
    Posts
    88
    Post Likes
    Variable speed vs multi-speed blowers:
    Could some explain what the difference is...
    i.e. do multi-speed blowers provide a similar level of comfort and savings as compared to a fully variable speed?

    or is it all or nothing?
    i.e there is very little difference between single speed blowers and multi-speed blowers against a variable speed.

    appreciate any thoughts/inputs

    thanks
    -shaum

  2. #2
    Join Date
    Nov 2003
    Posts
    28
    Post Likes
    Single and multi-speed blowers suck energy every time they start.

    The advantage of the variable speed motors, used in multistage equipment, is that they can ramp up and down with the required load, instead of everything starting up with a jolt.

    Multispeed blowers run constantly can be as comfortable, for a given load, but can't adjust to changing conditions.

  3. #3
    Join Date
    Jun 2004
    Location
    4H: Hot, Humid Houston H.O.
    Posts
    3,304
    Post Likes

    How A-S/Trane do it

    I am a homeowner who has an American Standard UD080R9V4K and its manual is revealing. At first thought, one would think the VS blower would ramp CFM up to high and down to low, and all points in between. Looking at the fan tables in the "Service Facts" manual page 13, it is not quite that way. Instead, there is a handful of discrete settings. One major benefit seems to be nearly constant CFM within a wide range of ESP conditions, compared to the other air handlers which vary CFM more depending on ESP.

    According to the table, a 3.5 ton AC could be set to deliver 1400 CFM, and it would remain in the range of 1380-1402 CFM with ESP as low as 0.1 inch w.c., and as high as 0.9.This is at 400 CFM/ton, 350 and 450 are selectable with DIP switches. You have surely seen more variety of equipment, but I have not seen such a range of ESP rated acceptable.

    The two-stage furnace runs at 860 CFM low, and 1243 CFM on high heating, at the "Medium" fan speed. One can select "Low" and "High", each setting is relatively flat no matter what the ESP.

    Other parts of the manual identify different speeds, but I do believe each is a fixed percentage of the main one. The famous "Comfort-R" feature provides for 50% and 80% of the main speed. A footnote tells us "Continuous Fan Setting: Heating or Cooling airflow is approximately 50% of selected Cooling value", and another says "For Variable Speed: low speed airflows are approximately 30% of listed values". I am not sure, but think that last item refers to their two-stage air conditioning.

    That's about it. You have a wide number of discrete choices which can be applied in your situation. Certainly the choices far outweigh the low-med-hi of the builder grade Consolidated furnace it replaced, and certainly it can keep up with 0.9 inch ESP within its specs. At one time I had downloaded manuals for several Trane models and I do not remember those capabilities being with the lower grade air handlers.

    Perhaps this amateur's view of things will inspire a pro to offer a fuller explanation. Or more concise.

    Hope this helps -- P.Student

  4. #4
    Join Date
    Sep 2005
    Posts
    685
    Post Likes
    The short version is VS saves electricity and adds comfort.
    Advantage of two gas is comfort and savings.

    The total pkg equals comfort and savings.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •