Results 1 to 4 of 4
  1. #1
    Join Date
    Oct 2005
    Posts
    2
    Post Likes

    Question

    A customer wants to heat his attached 3 1/2 car garage so that his pet can live there. should the unit have a outside air kit? the home is new and well insulated, and is located in the upper midwest. it will be a natural gas unit.Thanks for your input.

  2. #2
    Join Date
    Apr 2003
    Location
    Eugene, Oregon
    Posts
    1,210
    Post Likes
    Direct venting would be nice, depending on BTU rate and cubic feet of the garage you may not need outside air so long as the unit is at least 18" off the ground. All this depends on local codes.
    Proud supporter of Springfield Millers and Oregon Ducks.

  3. #3
    Join Date
    Oct 2005
    Posts
    2
    Post Likes
    the garage is 31/2 car with 10' ceilings. the unit will be suspended naer the ceiling. units ar avaliable with power venting only, and with power vent and outside combustion air. the home is new and well insulated, and the garage doors are weatherstriped. the area above the garage is living space. we expect to use a 60-75000 btu unit. my question really is because of the pet and tight construction is it best to use the outside combustion air model or is it a non issue? thanks again.

  4. #4
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,837
    Post Likes
    if garage is being kept on the cool side i would use a unit made for outside air, less chance of condensation problems.