We are adding 1,400 sqft to our existing 1,600 sqft house. The addition will be on the 2nd floor. How large a system should we be looking at? Would it make sense to have two different zones, one for the upstairs and one for the downstairs?
-
10-22-2005, 01:17 AM #2
Grumpy Old Man
- Join Date
- Apr 2003
- Posts
- 6,383
System sizing
2 systems or one system with two zones.
Helpful link
-
10-22-2005, 01:20 AM #3
Professional Member
- Join Date
- Aug 2004
- Location
- Tyler TX
- Posts
- 676
Try using the hvac calc software at the top of the page to find out what size equipment you will need. It is always best to have zone system or a separate system when you have a 2 story home.
HVAC Contractor, Tyler Texas.
-
10-22-2005, 07:06 AM #4
1400 sq ft addition, put a second unit in for it.
-
10-22-2005, 07:35 AM #5
Professional Member*
- Join Date
- Nov 2004
- Location
- SW FL
- Posts
- 5,263
Anywhere, CA
TWO SYSTEMS ARE REQUIREDOriginally posted by californiadreamer
We are adding 1,400 sq ft to our existing 1,600 sq ft house. The addition will be on the 2nd floor. How large a system should we be looking at? Would it make sense to have two different zones, one for the upstairs and one for the downstairs?
Factors which determine size:
Location ___
___ Location
______ Location
Design temperature is 101'F for Bakerfield
................... 95'F for Pasadena
................... 83'F for San Francisco
House and Window Orientations ___
... 50 feet x 28 feet or so
.50 or ___ feet faces West with 60 or ___Sq. Feet Windows
.50 or ___ feet faces East with 60 or ___
.28 or ___ feet faces North with 40 or ___
.28 or ___ feet faces South with 40 or ___
Window type__ Shading coefficient
Total Window area ~ 200 to 250 Sq. Ft.
___ Overhangs
___ Curtains or Blinds
Based on 75'F inside temp and above,
you may need 3 or 3.5 tons for Bakersfield.
like ~ 2.5 or 3 tons for Pasadena
like only 2 tons for San Francicso with 83'F design temp.
Other locations and orientations than asusmed
Who Knows?
In other words, ALL of the SPECIFICS ARE REQUIRED.
[Edited by dan sw fl on 10-22-2005 at 07:43 AM]Designer Dan
It's Not Rocket Science, But It is SCIENCE with "Some Art".

Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities
-
10-24-2005, 12:01 AM #6
Regular Guest
- Join Date
- Oct 2005
- Location
- Pasadena
- Posts
- 3
What Size System
Thank you to all those who replied. It sounds like I should get two systems. If I need a total of 3 tons, I assume I need two 1.5 systems? Is that correct?
Also, I have heard that leaks in the ducting system is very common how do I check whether my contractor has done a good job installing the ducts?
-
10-24-2005, 10:56 PM #7
Regular Guest
- Join Date
- Oct 2005
- Location
- Pasadena
- Posts
- 3
Re: Anywhere, CA
Dan, Thank you for such a thorough reply. It sounds like I should get two systems. If I need a total of 3 tons, I assume I need two 1.5 systems? Is that correct?
Also, I have heard that leaks in the ducting system is very common how do I check whether my contractor has done a good job installing the ducts?
TWO SYSTEMS ARE REQUIRED
Factors which determine size:
Location ___
___ Location
______ Location
Design temperature is 101'F for Bakerfield
................... 95'F for Pasadena
................... 83'F for San Francisco
House and Window Orientations ___
... 50 feet x 28 feet or so
.50 or ___ feet faces West with 60 or ___Sq. Feet Windows
.50 or ___ feet faces East with 60 or ___
.28 or ___ feet faces North with 40 or ___
.28 or ___ feet faces South with 40 or ___
Window type__ Shading coefficient
Total Window area ~ 200 to 250 Sq. Ft.
___ Overhangs
___ Curtains or Blinds
Based on 75'F inside temp and above,
you may need 3 or 3.5 tons for Bakersfield.
like ~ 2.5 or 3 tons for Pasadena
like only 2 tons for San Francicso with 83'F design temp.
Other locations and orientations than asusmed
Who Knows?
In other words, ALL of the SPECIFICS ARE REQUIRED.