Thread: use magnetic vent covers or not?
-
10-21-2005, 12:08 PM #1
Regular Guest
- Join Date
- Oct 2005
- Posts
- 3
I have a propane furnance, forced air. Two rooms are not used. Is it ok to block both the supply and return vents with magnetic vent covers in those rooms? It should reduce my heating costs correct? Thanks
-
10-21-2005, 12:19 PM #2
DO NOT USE THOSE!!!
It will cost you more money!
Your system is designed to move a certain amount of air and if you cut that flow down, the equipment will be working harder.
The fan will push the same amount against a greater static pressure and overwork the fan and overheat the exchanger.How tall are you Private???!!!!
-
10-21-2005, 12:57 PM #3
Banned
- Join Date
- Sep 2005
- Posts
- 685
He's right. You could cause an irrepairable over heat.
-
10-21-2005, 01:30 PM #4
Professional Member
- Join Date
- Feb 2004
- Location
- Central Kansas
- Posts
- 1,145
I believe these devices fall under snake oil energy saving sales tactics. These things will not save you and will in fact possibly cause damage as stated by others, costing you.
Don't confuse me with facts, my mind is already made up.
-
10-21-2005, 06:18 PM #5
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,640
it really depends on your system. if you have the minimum number of vents required, then covering anything could cause damage. on the other hand, if you have many more vents than the minimum, you could cover some with no ill effects. you could have a contractor look at your system and see if it is ok for you to cover a few vents.