    Guys checked charge which is correct.This is a 22 system 25 oz compressor at rated amps of 7 but compressor very ot suction is low 40lb head 200. I know there isnt enough to cool compressor. do you think suction valve bad.

  2. #2
    Join Date
    Jun 2011
    Location
    Rochester, NY
    Posts
    46
    Post Likes
    How do the guys know the charge is correct with those pressures. What's the inside and outside temp and how old is the system. What seer. Txv or orifice. Whats superheat and subcooling. Are filters and both coils clean?

  3. #3
    Join Date
    May 2010
    Location
    New jeresey
    Posts
    15
    Post Likes
    Thread Starter
    Charge removed and put back as per label ... water cooled.. 85 in 97 out.. filters clean... super heat 12 degrees .. also strainer clean. this is a heat pump unit.orifice metering device......

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    Doesnt sound like a bad compressor to me.


    A bad compressor would tend to have a high suction, not a low suction.


    As a side note, it isn't smart to insult those who are trying to help you.

  5. #5
    Join Date
    May 2010
    Location
    New jeresey
    Posts
    15
    Post Likes
    Thread Starter

    Confused

    Quote Originally Posted by jpsmith1cm View Post
    Doesnt sound like a bad compressor to me.


    A bad compressor would tend to have a high suction, not a low suction.


    As a side note, it isn't smart to insult those who are trying to help you.
    sorry wasnt thinking I apologize having bad day.....

  6. #6
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    More detailed system readings would tell a lot more about the problem.


    I've got a few ideas, but without a full set of readings, it isn't possible to guess.