Results 1 to 2 of 2
    Jan 2002
    Question
    I am installing a Nortec Resdelux steam humidifier. The instructions indicate that the humidifier, humidistat and high limit humidistat is wired to a DPDT AUX fan relay 24VAC, coil with two normally open contacts. This aux relay is then wired in parallel to the normal fan relay. I have a Carrier 58MVP furnace.
    Does anyone know where the normal fan relay cantacts are located in the furnace?
    Oct 2005
    Fairfax, VA
    Doesn't that unit have "HUM" terminals on the board? You could always use a current-sensing relay on a fan wire, controlling a dpdt contactor if nothing else is readily available.
    The wiring diagram will show the fan contacts.