Thread: Dirty Water From Steam Boiler

  1. #1
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    I just had my boiler for my single pipe residential steam heat system changed. My old boiler was a 45 year old PENCO that finally developed a leak in the casting and the new replacement boiler is a Burnham. I am now getting surging, bubbling and tons and tons of rust and sludge into the boiler. Why is this happening and how do I fix it? I have had people tell me to use a commercial chemical flush and other people say don't ever do this. I've also been told just to keep on boiling the water and flushing the system and it will eventually come clean. It seems like it will take forver.

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    42,886
    Post Likes
    Might want to ask the boys on http://www.heatinghelp.com as they are steam experts and willing to help homeowners with their systems.

  3. #3
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    I thought THIS site was for heating, too?

    I'm a steam expert, so they tell me, and I stopped posting over there when Constantin and the Viessman fans began tromping on every post from my customers.

    http://forums.invision.net/Thread.cf...#Message194614

    I won't bore you with the details of every incident, but that site is turning over to mostly homeowners advising homeowners.

    Back to HVAC on THIS site....

    That boiler could use a surface skimming to remove oils from the top of the water. Draining the water out only coats the walls of the boiler with the oils.

    Draining out the dirty water is a good idea, it just won't remove the oils.

    Make SURE the piping diagram in the manual illustrates YOUR boiler piping, or the water level will be all over the place. If your equalizer is undersized (or ANY pipe), the water will head out.

    Make sure the boiler isn't TOO BIG, or it will make steam faster than the steam piping can handle and the water will leave the boiler out the return piping.

    Make sure the boiler itself isn't overfired (Fuel pressure and nozzle or orifice size).

    If you have wet returns, be sure that they are open, and not partly plugged.

    Noel

  4. #4
    Join Date
    Jan 2002
    Posts
    1,196
    Post Likes
    yup what Noel said.

    Don't mind Connie myself, but a certian V affectionado irritates me w/ his constant crowing about how great they are, and how there are no other options, except Crown.

    I don't post there too much either, because I got tired of constant prayer requests, donations, and causes..and all the implied and real obligations that go along w/ all that stuff. I want heating discussions, not pressure to follow the herd..

  5. #5
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    Thread Starter
    Thanks so much for your ideas Noel. I have been skimming through the pressure relief valve which I assume is taking water from the top of the boiler. I blow it off when there is a full head of steam and add fresh water at the same time. The boiler is gas fired so I don't have to worry about overfiring. The boiler size was calculated by two companies so I assume it's the correct size for the radiation. The equalizer looks good to me as does the hartford loop but I have no way of really knowing. The company that installed it just 5 months ago is out of business so they won't be any help. It's always my luck when I look for a contractor to end up in this kind of trouble.

  6. #6
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    Skimming

    Skimming is done with a QUIET water surface, with a flow the size of a pencil. It's done for an hour to eight or ten hours. It's done with the water 200° F , but with the burner off.

    It's done by allowing a very small trickle of fresh water in, while letting the oil flow through a HORIZONTAL tapping in a side of the boiler, so that the oil can freely leave through a nipple that is less than half full.

    Reheat the boiler every so often. It's the smooth water surface that is very hot that removes the most oils.

    Here's a picture...

    http://www.slantfin.com/spec-galaxygxh.html

    Noel

    [Edited by Noel Murdough on 10-19-2005 at 02:50 PM]

  7. #7
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    Thread Starter
    The only way I can figure to do this would be to unscrew the pressure relief valve that is near the top of the boiler and thread in a length of 3/4" pipe as a drain. Then I can heat the boiler to just below the boiling point and slowly add fresh water at the bottom of the boiler. This will probably have to be done several times or more as I most likely will be dragging new crud down from the old pipes and radiators. How does this sound? Thanks again for your help.

  8. #8
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    that'll be worth trying

    look for an oil sheen on the water that comes out.

    Noel

  9. #9
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    Thread Starter
    I don't think it's a surface oil problem. I am still getting gallons of rust & sludge out of the system after I bring it up to steam.(running at 2.5 psi) I am draining the crap out and refilling with fresh water. I hope all my radiators and pipes are not disintegrating from the inside out. I am still assuming that eventually this will slow down and stop. It has to. There are no leaks in any pipes or radiators that I can see. I imagine this was all caused because I went from a large water capacity boiler to a new lower water capacity steam boiler. This looks like it may be an all winter project and I hope I don't somehow damage the new boiler in the process.

  10. #10
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    whatever you say.

    Your symptoms still tell me that you are throwing gallons of water up into that system, and not gentle, light, fluffy steam, which would condense and trickle back to the boiler.

    Noel

  11. #11
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    Thread Starter
    Do you think it's an improper installation? It looks good according to the Burnham manual. The "A" dimension is about 45 inches. What else would push water up the pipes? The person who installed it claimed to be a steam expert, but I know I'm not. I would not be a to happy if the boiler was not installed correctly and I understand the people who did the installation are out of business. This was only 6 moths ago.

  12. #12
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    It sounds like oily water, to me.

    Noel

  13. #13
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    Thread Starter
    Much thanks again Noel. I know what I'll be doing this weekend. I will let you know how it works after I skim the surface.

  14. #14
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    Look at these pictures

    They are the same boiler, the same piping, the same water, and the same pressure.

    The first ones are with clean water. Notice the light, fluffy steam, with NO water carried with it. The steam vapor RISES into the system.

    The others have a tablespoon of cooking oil added to the boiler water. That's the ONLY difference. This is what I think is bringing back the crud.

    Noel







    The next ones are with the oily water.






  15. #15
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    Thread Starter
    That's amazing. That gives me hope that I might have heat this winter and didn't spend $7,000 and hours of indigestion for nothing.

  16. #16
    Join Date
    Sep 2004
    Posts
    654
    Post Likes
    Originally posted by dtlithonia1
    I don't think it's a surface oil problem. I am still getting gallons of rust & sludge out of the system after I bring it up to steam.(running at 2.5 psi)
    2.5 psi of steam?....remember, setting the pressure-trol to 2.5 is the cut-in pressure, the cut-out pressure is the differential setting plus the 2.5 psi. Typical pressure-trol setting on the diff is 1 psi, so in effect you could have 3.5 psi of steam pressure in the system....OUCH. That's ALOT of steam energy that is just aching to make noise and stir up alot of sludge. I'm no steam guru, so hopefully someone who is can proof read this. For a residential boiler I run maybe 1 psi of steam and set the diff really low, maybe .5 psi tops. Lower setting on the pressure-trol has got to save fuel too I would think.


  17. #17
    Join Date
    Apr 2004
    Posts
    395
    Post Likes

    Hmm

    Priming and surging is cased by the oil in the boiler from piping ect. You can try a few things skimming, white vinegar or Scot but I would call the co back.
    Tin Knockers BANG for a living

  18. #18
    Join Date
    Oct 2005
    Posts
    24
    Post Likes
    Thread Starter
    The only way I can skim is to unscrew the pressure safety since its taped in near the top of the boiler into a 3/4" hole. Do I have to do this hot or cold? If I added vinegar to the water how much would I add and what would this do? Thanks. Oh the company that just put in the boiler is out of business.

  19. #19
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285
    Post Likes

    vinegar is for changing the pH

    How much is determined by testing the pH before and after. It cures OTHER problems.

    Shoot for an 8 or 9 pH.

    Noel

  20. #20
    Join Date
    Nov 2003
    Posts
    51
    Post Likes
    noel
    great illustrations very impressed

    make sure if you take the relief valve out to skim the boiler put a tee in and reinstall the pressure relief valve god forbid something was to happen to you and that boiler was operating without a relief valve you never know

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •