    Look at these pictures

    They are the same boiler, the same piping, the same water, and the same pressure.

    The first ones are with clean water. Notice the light, fluffy steam, with NO water carried with it. The steam vapor RISES into the system.

    The others have a tablespoon of cooking oil added to the boiler water. That's the ONLY difference. This is what I think is bringing back the crud.

    Noel







    The next ones are with the oily water.






  2. #15
    That's amazing. That gives me hope that I might have heat this winter and didn't spend $7,000 and hours of indigestion for nothing.

  3. #16
    Join Date
    Sep 2004
    Posts
    654
    Originally posted by dtlithonia1
    I don't think it's a surface oil problem. I am still getting gallons of rust & sludge out of the system after I bring it up to steam.(running at 2.5 psi)
    2.5 psi of steam?....remember, setting the pressure-trol to 2.5 is the cut-in pressure, the cut-out pressure is the differential setting plus the 2.5 psi. Typical pressure-trol setting on the diff is 1 psi, so in effect you could have 3.5 psi of steam pressure in the system....OUCH. That's ALOT of steam energy that is just aching to make noise and stir up alot of sludge. I'm no steam guru, so hopefully someone who is can proof read this. For a residential boiler I run maybe 1 psi of steam and set the diff really low, maybe .5 psi tops. Lower setting on the pressure-trol has got to save fuel too I would think.


  4. #17
    Join Date
    Apr 2004
    Posts
    395

    Hmm

    Priming and surging is cased by the oil in the boiler from piping ect. You can try a few things skimming, white vinegar or Scot but I would call the co back.
    Tin Knockers BANG for a living

  5. #18
    The only way I can skim is to unscrew the pressure safety since its taped in near the top of the boiler into a 3/4" hole. Do I have to do this hot or cold? If I added vinegar to the water how much would I add and what would this do? Thanks. Oh the company that just put in the boiler is out of business.

  6. #19
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285

    vinegar is for changing the pH

    How much is determined by testing the pH before and after. It cures OTHER problems.

    Shoot for an 8 or 9 pH.

    Noel

  7. #20
    Join Date
    Nov 2003
    Posts
    51
    noel
    great illustrations very impressed

    make sure if you take the relief valve out to skim the boiler put a tee in and reinstall the pressure relief valve god forbid something was to happen to you and that boiler was operating without a relief valve you never know

  8. #21
    My question now would be--- if I skimmed and flushed and was fairly sure there was no oil or dirt in the boiler but everytime the boiler tried to make steam it was still pushing water up the pipes (and of course bringing down dirt and rust) what would I do next?

  9. #22
    Join Date
    Jan 2002
    Location
    New Hampshire
    Posts
    1,285

    let's not play "if".

    What are your actual symptoms? Have you checked a sample of the water that came off the top of the boiler? Is there oil on it?

    What else have you checked, so far?

    Noel

  10. #23
    Join Date
    Jul 2001
    Location
    Buffalo N.Y.
    Posts
    1,571
    Originally posted by casturbo
    Originally posted by dtlithonia1
    I don't think it's a surface oil problem. I am still getting gallons of rust & sludge out of the system after I bring it up to steam.(running at 2.5 psi)
    2.5 psi of steam?....remember, setting the pressure-trol to 2.5 is the cut-in pressure, the cut-out pressure is the differential setting plus the 2.5 psi. Typical pressure-trol setting on the diff is 1 psi, so in effect you could have 3.5 psi of steam pressure in the system....OUCH. That's ALOT of steam energy that is just aching to make noise and stir up alot of sludge. I'm no steam guru, so hopefully someone who is can proof read this. For a residential boiler I run maybe 1 psi of steam and set the diff really low, maybe .5 psi tops. Lower setting on the pressure-trol has got to save fuel too I would think.


    The 2.5 would be the cut-out, minus differential for cut-in.
    The problem with pressure controls is that there not very accurate, close though.


    Noel is right about what-if's, without some certainty as to the water quality and the boiler internal condition it's speculation as to the issue.

    One thing, if the water is hard it's most likly more on the acidic side.
    A high PH will cause surging/foaming.
    Oil will cause carryover, slight priming with lo pressures. The oil increases the water surface tension causing the steam bubbles to explode through the layer with much greater velocity. Oil in the water can be confused with a hi PH level and the two are often confused.

    Also read that the guy is empting and re-filling with fresh water, a good idea, if possible, is to use not cold tap water but heated water. Cold water holds much more disolved oxygen than hotter water.
    With residential this isn't always possible, but even 120 degrees from the hot water tank is better than cold tap water for a skimming.
    The idea is to remove as much O2 as possible before steaming.

    [Edited by bobby7388 on 10-31-2005 at 10:39 PM]

  11. #24
    Join Date
    Jan 2002
    Location
    tip of the mitt
    Posts
    1,974
    When you figure you're done skimming pour some water in a pan and boil it on your stove if it foams keep skimming.
    I have my own little world. But it's OK...they know me here.

  12. #25
    Join Date
    Nov 2003
    Posts
    28
    Just to add a little to the discussion here: Remember that everytime you introduce fresh water into the system you are introducing air and contaminants. This adds to the crud in the water.

  13. #26
    Hi thanks again Noel and to all who have helped. I spent two days surface skimming and the system is working much, much better. I skimmed untill the water looked clean enough to drink and a sample boiled quietly on the stove. But I'm still getting some surging and bringing new contaminents into the boiler and it looks like it will get worse after a period of use. I also set the pressuretrol to 2psi and the differential to one half pound. It says the differential is subtractive. That means the boiler should cut out at 2 lbs and back in at one half pound if I am still calling for heat. Is that right? Also someone suggested a boiler cleaning additive and someone else said never to use anything like that. All the radiators in the house now do get warm although I know I still have to do some balancing once I get rid of the surging. And I am still not sure the pressuretrol is set correctly. I can see by the pressure gauge that I am still getting a couple of pounds in the system even though the main vents and all the radiator vents are new.

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event