    Hi all, read a post here a few days ago about a furnace being to large. One of the replies was to partially close the gas supply valve. What would be the consequences of doing this.Harm the heat exchanger? gas valve ?etc.

  2. #2
    Join Date
    Feb 2005
    Location
    Richmond
    Posts
    482
    Post Likes
    Gas valve is NOT to be partilly closed to regulate heat strength. It is designed to be either fully opened or fully closed.

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    BOOM

    Please don’t mess with the gas valve, Shut off valve or the system in general. No one here can see your unit. IT MUST BE LOOKED AT BY A HEATING CONTRACTOR AT YOUR HOME.

  4. #4
    Join Date
    Oct 2004
    Location
    Tyler, TX
    Posts
    3,400
    Post Likes
    Originally posted by hemitom
    Hi all, read a post here a few days ago about a furnace being to large. One of the replies was to partially close the gas supply valve. What would be the consequences of doing this.Harm the heat exchanger? gas valve ?etc.
    Don't do it.

    Who told you the furnace is too large?
    RSES Certificate Member Specialist

    Southwest Regional Association of RSES Secretary, 2017

  5. #5
    Join Date
    Dec 2004
    Posts
    24
    Post Likes
    Thread Starter
    Its not my furnace just a post i read here, no one really gave a response to the question in the post. Jultza, or any other hvac pro,why don't you explain why this is so dangerous so people won't try it. this is the response i was looking for (a warning to others as to why not to do this) thank you.

    [Edited by hemitom on 10-18-2005 at 08:13 PM]

  6. #6
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes
    And this is the EXACT reason THAT post should have been DELETED!

    Now, along with this one.... SOMEONE is going to TRY IT!

  7. #7
    Join Date
    Jun 2000
    Location
    WYO
    Posts
    2,187
    Post Likes
    lowers design gas pressure to manifold which may cause flashbacks into burners and delayed ignition (fires and explosions)and,raises carbon monoxide levels and can prevent proper venting of flue gas (sickness or death).
    two reasons I can think of not to do that.
    Fix the problem correctly.If you dont know how, get someone that does. Thats a big no-no in our trade.

  8. #8
    Join Date
    Dec 2004
    Posts
    24
    Post Likes
    Thread Starter
    Thanks contactor, this is a response that should have been give to the original post . this is something that will make a home - owner, renter, or whoever not try this. not a reply like boom! or blow up your house etc. a straight forward common sense reply thanks again.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •