Build up system with undersized condenser coil
I have a one year old Frankenstein build up system with an undersized condenser coil. Does anyone know how I would possibly determine how many BTU's of additional condenser coil are required? And no, there is no make or model of the existing coils. All I can say is there are two 40 tons Copeland’s running with 404a.
-
07-11-2011, 08:18 PM #2
Professional Member
- Join Date
- Apr 2007
- Location
- Pa
- Posts
- 738
how do you know the condenser is undersized?
-
07-11-2011, 11:45 PM #3
Professional Member*
- Join Date
- Feb 2010
- Location
- Cal
- Posts
- 1,323
US coil has a design cd they can mail to you. Toy around with it~ area, ckts, passes, fpi, and you should have a better handle on things.
Gather you have ruled out assembly, direction and piping errors.
No sub cooling?
-
07-12-2011, 12:02 AM #4
Professional Member
- Join Date
- Sep 2010
- Location
- San Diego
- Posts
- 63
Undersized Condenser coil
The sub-cooling is good under normal ambient conditions but it drops when the outdoor air temp gets around 100 deg. I'm going to check it for non-condensable tomorrow just to rule it out. The condenser coil is right next to the compressors but I'll give the piping a check up.