Thread: Lennox 12ACB48- Help
-
07-12-2011, 10:10 PM #14
Regular Guest
- Join Date
- Jul 2011
- Posts
- 15
-
07-12-2011, 10:22 PM #15
-
07-12-2011, 10:26 PM #16
-
07-12-2011, 10:47 PM #17
Regular Guest
- Join Date
- Jul 2011
- Posts
- 15
-
07-13-2011, 12:00 AM #18
No prices allowed in post.
-
08-26-2011, 08:11 PM #19
Regular Guest
- Join Date
- Jul 2011
- Posts
- 15
OK So the tech came about a month ago and said the coil was dirty and it needed to be cleaned. I let him clean it and the system ran fine for about a month now and it just did the same thing again. Fan running, but compressor not and not cooling. I shut the system off and sprayed it with a water hose and waited about 10 minutes and low and behold it is cooling again right now.
What could this be?
-
08-26-2011, 08:22 PM #20
Could be a bad/weak electrical component. Call that same company back, and tell them its doing it again.
-
08-26-2011, 09:57 PM #21
Get a good company to come out and test out your components. Also find out your superheat, subcooling and if there is a chart on the condenser, see if the condenser is performing accordingly to the temperature / pressure chart. Other electrical parts can be bad are like run capacitor, start capacitor or some relay system maybe in place. Ask them to test the compressor also.
-
08-26-2011, 10:18 PM #22
Regular Guest
- Join Date
- Jul 2011
- Posts
- 15
Where do I get this chart?
-
08-27-2011, 08:37 AM #23
Look on your condenser, unless the label has faded away.
-
08-27-2011, 05:46 PM #24
Regular Guest
- Join Date
- Jul 2011
- Posts
- 15
My uncle came over and added a hard start kit. We are also going to replace the run capacitor next week.
I dont see the chart.
-
09-14-2011, 06:46 PM #25
Regular Guest
- Join Date
- Jul 2011
- Posts
- 15
Well I just came home and it quit again. Fan was spinning but compressor was not running. Where to look now?
-
09-14-2011, 08:54 PM #26
you NEED help!!!
Don't annoy the combat veteran!!!!
All gave some - Some gave ALL