Results 1 to 10 of 10

Thread: cyles per hour

  1. #1
    Join Date
    Sep 2004
    Posts
    67
    Post Likes
    I am programming my new Honeywell vision pro 8320 and at one point it asks how many cycles per hour do I want??? I have a heat pump with a 96 % gas furnace as back up. It suggests a setting of 3 cph for this set up so thats what I went with.

    What cycles are we talking about her Vern? (you will have to be plus 55 to know about the reference to Vern).

    Thanks, North

  2. #2
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    how many times the unit comes on(cycles)per hour.

    I dont know that much about programing anything,but I can tell you that is a good feature to have.I am assuming it is there to prevent short cycles and will override if longer run cycles are called for on cold days.Three sounds good.

  3. #3
    Join Date
    Sep 2004
    Posts
    67
    Post Likes
    Thread Starter
    Okay...........so then if I have the anticipator set for 1 degree celcius and the temperature varies more than that, for more than 3 times in one hour then the furnace won't come on??
    Am I followning this correctly?

    North

  4. #4
    Join Date
    Nov 2004
    Posts
    2,928
    Post Likes
    now you are confusing me.hopefully someone who really knows this stuff will come along ...there is a bunch of them here.

    somehow the programing makes the unit come on a maximum of three times per hour.that is good because it is more econmical and causes less wear to equipment.how the programing does it? i dont know what to say...it manipulates the readings to cause the desired outcome.

    now having said that,someone might come along with a more informed answer.that's the way it works here.

  5. #5
    Join Date
    Sep 2004
    Posts
    67
    Post Likes
    Thread Starter

    Talking

    Well one thing I have found from lurking on this board is that there is certainly no lack of opinion..........LOL!

    Anyone out there who can clear this up?..........hello!

  6. #6
    Join Date
    May 2004
    Location
    Austin, TX
    Posts
    1,852
    Post Likes
    I have a couple of Vision Pros installed at my home,
    and if it is set to 3 cycles per hour, that is what
    it will allow.

    If the temperature varies more that three cycles, it
    will delay, or hold on to average out the cycles. So
    at times your temperature will fluctuate beyone this
    1 oC setting.

  7. #7
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    most rotating motors & compressors ( X for vehicles ) rated for no more than 4 starts per hour!
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  8. #8
    Join Date
    Aug 2004
    Location
    Great White North
    Posts
    92
    Post Likes
    Northof49: Or should I say "Hey, Vern. It's your good buddy Ernest, here". And I'm quite a ways from 55... If you have the cycles per hour too high, the thermostat will narrow the differential between "call for heat" and "heat satisfied". Basically, if you allow it too many cycles per hour, it will use that to run the furnace up to that many times per hour to keep the set temp. So, if you say six per hour and set the temp at 21 deg C, it might set the range to 20.8 (call for heat) and 21.3 (heat satisfied). If you say three per hour, it might set the range to 20.5 to 21.5. So, the more cycles, the less drift allowed from the set temp. The less cycles, the more drift allowed from the set temp.

    i.e. My father-in-law had a VisionPro thermostat installed last winter. I was over after that and would hear his furnace start and run for only about five to 10 minutes (can't remember exactly). Regardless of how long(or short) it ran, I could tell it was short cycling. What was happening was that the thermostat was trying to keep the temperature as close to the set point as it could. This was all due to the thermostat installer dialing up 6 cycles per hour. Once I got my hands on it, I set it to 3 or 4 (can't exactly recall). This made the thermostat widen range in temp before it would "call for heat" or say "enough heat". Now it cycles and runs for 15-20 minutes each time.

  9. #9
    Join Date
    Apr 2005
    Location
    Tampa, Florida
    Posts
    1,682
    Post Likes
    The other thing to keep in mind is that longer cycles = better efficiency. The first few minutes of operation (heating or cooling) are the most inefficient time. You're waiting for the heat exchanger & ductwork to warm up or waiting for the evaporator coil & ductwork to cool down. With single stage AC's, it can be up to 10 minutes before everything's cooled down to the optimum temperature.

    As posted by others, longer cycles = less comfort (theoretically). And yes, if you set it for 1 cycle per hour, there's a good chance that comfort won't be all that great. BUT, 3 cycles per hour would mean ~20 mins per "cycle". Now, the cycles per hour is the maximum # of cycles the stat will do, and it will do only 1 cycle per hour (or less) if need be (extreme heat/cold outside).

  10. #10
    Join Date
    Sep 2004
    Posts
    67
    Post Likes
    Thread Starter
    Got it guys.........thanks a million.

    North

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •