    Latent capacity

    Is latent capability generally reduced with larger evaporators? I have a multi split mini split system with three evaporators that has 180% larger evaporator size. Does thid kill the latent capability?

  2. #2
    Join Date
    Feb 2010
    Location
    In a machine room
    Posts
    7,953
    Post Likes
    Do you mean the indoor unit BTU ratings are 180% of the outdoor unit capacity? This is not usually allowed.

    Do you have model numbers of the indoor and outdoor units?

    Mini splits usually run very cold coils and have superior latent capacity.
    Worry is a really gross misuse of one's imagination. -- PHM

  3. #3
    Join Date
    Jul 2000
    Location
    NW IL.
    Posts
    3,942
    Post Likes
    Floral cases have larger evaporators to cool the air faster to keep the humidity levels high.
    Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.

  4. #4
    Join Date
    Feb 2010
    Location
    In a machine room
    Posts
    7,953
    Post Likes
    I think he is talking about mini splits.
    Worry is a really gross misuse of one's imagination. -- PHM

  5. #5
    Join Date
    Jun 2011
    Location
    Brooklyn, NY
    Posts
    29
    Post Likes

  6. #6
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,405
    Post Likes
    Quote Originally Posted by ChaseAir View Post
    Is latent capability generally reduced with larger evaporators? YES.I have a multi split mini split system with three evaporators that has 180% larger evaporator size. Does thid kill the latent capability?Doesn't kill it, but does greatly reduce it.
    I would see if your setup in a match. If it is, then there should be some published S/T ratings.

  7. #7
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,869
    Post Likes
    I think the evap. coil dimensions alone will not affect the sensible to latent ratios if its capacity match the load, a larger coil with more fins per inch will dehumidify better cause the large surface for condensation to take place, besides the coil area there are many other factors playing a role in latent heat removal like air velocity,coil temperature and run time.

  8. #8
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,869
    Post Likes

  9. #9
    Join Date
    Jun 2011
    Location
    Brooklyn, NY
    Posts
    29
    Post Likes
    Quote Originally Posted by hvacpope View Post
    from the school of cut and paste
    yeap...
    hey, not my game, still learning here, give me same time... Luckly, Darrel U is a GREAT teacher!

  10. #10
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,595
    Post Likes
    Thread Starter
    Quote Originally Posted by chuckcrj View Post
    Do you mean the indoor unit BTU ratings are 180% of the outdoor unit capacity? This is not usually allowed.

    Do you have model numbers of the indoor and outdoor units?

    Mini splits usually run very cold coils and have superior latent capacity.
    The strange thing is the manual says you can do it, but it all makes sense now. As rated, this mini split system has a 15% latent capacity. That is not superior to many regular split systems that have 27% latent capacity.


    Hooked up my old system again today. The moisture is pouring out.

  11. #11
    Join Date
    Feb 2010
    Location
    In a machine room
    Posts
    7,953
    Post Likes
    Make and model?
    Worry is a really gross misuse of one's imagination. -- PHM

  12. #12
    Join Date
    May 2009
    Location
    Jacksonville FL
    Posts
    4,595
    Post Likes
    Thread Starter
    Quote Originally Posted by chuckcrj View Post
    Make and model?
    Cmh1972a
    2 7700 btu kmhs7720 and
    1 18000 btu kmhs1872

    Swear I read somewhere in the tech data you could do this, did not think about what this would do to the latent capacity. In Florida latent capacity is real important.

  13. #13
    Join Date
    Feb 2010
    Location
    In a machine room
    Posts
    7,953
    Post Likes
    According to Sanyo they say up to 24,830 btu max indoor units capacity for the CMH1972A outdoor unit.

    Edit: just saw another pdf that said you're OK with up to 200% of outdoor capacity, so you're probably OK.