Results 1 to 13 of 14
Thread: Latent capacity
    May 2009
    Jacksonville FL
    Latent capacity
    Is latent capability generally reduced with larger evaporators? I have a multi split mini split system with three evaporators that has 180% larger evaporator size. Does thid kill the latent capability?
    In a machine room
    Do you mean the indoor unit BTU ratings are 180% of the outdoor unit capacity? This is not usually allowed.
    Do you have model numbers of the indoor and outdoor units?
    Mini splits usually run very cold coils and have superior latent capacity.
    Worry is a really gross misuse of one's imagination. -- PHM
    Jul 2000
    NW IL.
    Floral cases have larger evaporators to cool the air faster to keep the humidity levels high.
    Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.
    In a machine room
    I think he is talking about mini splits.
    Jun 2011
    Brooklyn, NY
    Jun 2006
    New Jersey
    Quote Originally Posted by ChaseAir View Post
    Is latent capability generally reduced with larger evaporators? YES.I have a multi split mini split system with three evaporators that has 180% larger evaporator size. Does thid kill the latent capability?Doesn't kill it, but does greatly reduce it.
    I would see if your setup in a match. If it is, then there should be some published S/T ratings.
    Apr 2005
    where the beer flows like wine
    I think the evap. coil dimensions alone will not affect the sensible to latent ratios if its capacity match the load, a larger coil with more fins per inch will dehumidify better cause the large surface for condensation to take place, besides the coil area there are many other factors playing a role in latent heat removal like air velocity,coil temperature and run time.
    Apr 2005
    Jun 2011
    Brooklyn, NY
    Quote Originally Posted by hvacpope View Post
    from the school of cut and paste
    yeap...
    hey, not my game, still learning here, give me same time... Luckly, Darrel U is a GREAT teacher!
    May 2009
    Jacksonville FL
    Quote Originally Posted by chuckcrj View Post
    The strange thing is the manual says you can do it, but it all makes sense now. As rated, this mini split system has a 15% latent capacity. That is not superior to many regular split systems that have 27% latent capacity.
    Hooked up my old system again today. The moisture is pouring out.
    In a machine room
    Make and model?
    May 2009
    Jacksonville FL
    Make and model?
    Cmh1972a
    2 7700 btu kmhs7720 and
    1 18000 btu kmhs1872
    Swear I read somewhere in the tech data you could do this, did not think about what this would do to the latent capacity. In Florida latent capacity is real important.
    In a machine room
    According to Sanyo they say up to 24,830 btu max indoor units capacity for the CMH1972A outdoor unit.
    Edit: just saw another pdf that said you're OK with up to 200% of outdoor capacity, so you're probably OK.