    fair enough. Thanks Doc. I would think the problem you refer to would not be as much of a problem unless you were attemping to pull your total amount of return through a single space. This return may only account for approximately 1/5 of the total air return.
    Everyone has a purpose in life..........even if it's to be a bad example.

    Seek first to understand, before seeking to be understood.

  2. #15
    Join Date
    Jun 2001
    Location
    Louisville, KY
    Posts
    12,189
    90° adjustable elbow is 10 equivalent feet. So, the jumper would be 41 or 42 equivalent feet presuming you use sheet metal pipe between the elbows.