+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast
Results 21 to 40 of 52

Thread: 30 ton split R-22 to 410a

  1. #21
    Join Date
    Mar 2011
    Posts
    1,076
    Post Likes
    Interesting. I guess it would cycle considering the pounds per hour of refrigerant circulated -vs- 22.

    The capacity may have went up significantly.

    It may end up like swiss cheese shortly.

    We have trouble keeping gas in equip. designed for 22 running 22.

    Good Luck~

  2. #22
    Join Date
    Sep 2005
    Posts
    58,704
    Post Likes
    Quote Originally Posted by AiResearch View Post
    Interesting. I guess it would cycle considering the pounds per hour of refrigerant circulated -vs- 22.

    The capacity may have went up significantly.

    It may end up like swiss cheese shortly.

    We have trouble keeping gas in equip. designed for 22 running 22.

    Good Luck~
    Yeah, I am interested to hear what issues this repair/upgrade/modification encounters.

    AirResearch.. For those of us that do not work with large equipment.. what is that in your avatar (picture) THX.
    GA-HVAC-Tech

    Your comfort, Your way, Everyday!

    GA's basic rules of home heating and AC upgrades:
    *Installation is more important than the brand of equipment
    *The duct system keeps the house comfortable; the equipment only heats and cools (and dehumidifies)
    *The value of comfort, over the long term; leave economic choices behind!
    Choose your contractor wisely!

  3. #23
    Join Date
    Mar 2011
    Posts
    1,076
    Post Likes
    Quote Originally Posted by ga-hvac-tech View Post
    Yeah, I am interested to hear what issues this repair/upgrade/modification encounters.

    AirResearch.. For those of us that do not work with large equipment.. what is that in your avatar (picture) THX.
    That is a variable pitch vaneaxial fan manufactured by Joy.

    They can be used for conditioned supply air or ventilation.

    They have high static pressure and volume capabilities.

    Generally applied when airflows and pressures exceed 40,000 cfm or more and 3.5 in. or more.

    Straight line airflow and use less space than a housed backward incline fan.

    Vanes downstream of the fan blades will staighten the circular air motion before entering the duct.

    Seen a few , never touched one.

  4. #24
    Join Date
    Jan 2006
    Location
    Seattle, Wa
    Posts
    116
    Post Likes
    Interesting thread, how is the equipement operating. An update would be great!

  5. #25
    Join Date
    Apr 2005
    Posts
    83
    Post Likes
    What's the address and startup date, I want to see this!

  6. #26
    Join Date
    Nov 2005
    Posts
    1,351
    Post Likes
    Thread Starter
    Well things were working well, then compressor noise started recently, and then mechanical failure. Looks as if Trane is having some problems with their 15 ton scrolls. The factory is running out of them, there have been several replacements around the country. I have to replace both compressors, Trane is covering the compressors, but not any labor allowance. Has anybody else run into this?
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!

  7. #27
    Join Date
    Aug 2012
    Location
    Midwest
    Posts
    2
    Post Likes
    Have you thought about the new lubricant? It will wash all the old wax left over from the mineral oil into the expansion devices. The higher pressures are also a huge concern.

  8. #28
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Moved to Tech to Tech commercial forum.

  9. #29
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Quote Originally Posted by ascj View Post
    Last I checked 410a and 407c is not far off in price.
    How about today's prices?

  10. #30
    Join Date
    Mar 2011
    Location
    Long Beach, CA
    Posts
    492
    Post Likes
    I guess that that my prayer for you is a little too late. But now you must continue with a little hope.
    As for the failure this was to be expected. As the others have stated, R-22 and 410A components should never be mixed. The equipment is not interchangeable. You now have a monster out of control.
    It sounds like you have a tandem scroll compressor arrangement which will normally require replacement of both compressors. Sounds easy enough Huh?

    I don't think so. Your compressor failed because a lack of oil. This was evident from the noise and the locking up of the scrolls. Now you will have to first clean up the mess. There are now fine metal micron fragments in the system which must be removed or expect another quick failure. You know the routine with a high capacity clean up suction filter/drier. You will also need to perform an acid test.

    Having left behind some mineral oil and mixing with POE oil has resulted in the form of two liquids. This is a direct result of oil loss.

    As for the remedy you will need to consider operation in a part loaded condition. The installation of a hot gas bypass line will need to be installed so that proper circulation of oil can be maintained and returned to the compressor. Liquid line size will need to be evaluated so as to maintain a minimum velocity of 260 feet per minute and a recommended maximum of 400 feet per minute. Suction Line size may need to be at least 1-5/8 or maybe even 2-1/8 so as to maintain proper oil return

    REMEMBER: With 2 stage units you must look at the suction line velocity at reduced capacity to insure velocity remains above 1000fpm on suction risers. If it does not, reducing the riser size by one size will correct the problem


    I will send you a sizing chart as an example for your use in the next post:
    If you want I can email it as an excel file.

    In addition I would remove the suction accumulator and install one sized correctly for your application. It sounds like you have a single circuit with one TXV.

    The other problem that you will have is that when one compressor is running it will have the tendency to draw oil from the compressor which is off by means of oil misting. You will have to install a crankcase heater and possibly two so as to prevent this from happening.

    The head pressure will also need to be maintained at a minimum set point and controlled by a speed controller such as a Penn/Johnson VFD 66 Drive and with the use of a pressure transducer P499.

    I can go on but not tonight.

    Troubleshooting is not part of the repair..............understand the symptoms and you will find a solution.

  11. #31
    Join Date
    May 2002
    Posts
    949
    Post Likes
    I know of some that were supposed to have POE and accidentally shipped with mineral ....

    Trans paid 100% and provided the labor as well....

    Shhhhhh....

  12. #32
    Join Date
    May 2002
    Posts
    949
    Post Likes
    I think the biggest point missed here is R22 equipment and components are NOT safety rated for the higher pressure of R410a...

    I'm converting my service van from gasoline to diesel to save money ...any ideas ....

    Everybody who continues to perform work like this ,thanks for the future work....

    And yes ,I know the OP.had his hands tied ,,,as I have in in the past....

  13. #33
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by mikeacman View Post
    I think the biggest point missed here is R22 equipment and components are NOT safety rated for the higher pressure of R410a...

    I'm converting my service van from gasoline to diesel to save money ...any ideas ....

    Everybody who continues to perform work like this ,thanks for the future work....

    And yes ,I know the OP.had his hands tied ,,,as I have in in the past....
    The evap coils that were made 30 years go, and most other evap coils made pre 13 SEER min were made thicker then a coil made/rated for R410A today.
    Line sets today, aren't made any thicker then line sets 10, 20, 30 or more years ago.

    The condenser coil of a new R410A unit has a thinner wall then the old evap coils do.

  14. #34
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Your more than likely correct ...

    but they still aren't rated from a liability standpoint ...
    most evaps like that I've seen are pressure rated at 150 to 300 psig .
    Dump a full charge in a room from a blowout and make people sick and see what happens when lawyers get involved....
    That will never happen .... Famous last words

    Absolutely no disrespect intended ,just my personal opinion

  15. #35
    Join Date
    May 2002
    Posts
    949
    Post Likes
    And with R22 options why go 410a???

  16. #36
    Join Date
    Apr 2010
    Location
    Minnesota
    Posts
    536
    Post Likes
    Quote Originally Posted by allstar08 View Post
    Well things were working well, then compressor noise started recently, and then mechanical failure. Looks as if Trane is having some problems with their 15 ton scrolls. The factory is running out of them, there have been several replacements around the country. I have to replace both compressors, Trane is covering the compressors, but not any labor allowance. Has anybody else run into this?
    Thank you for this thread, it's been educational.

  17. #37
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by mikeacman View Post
    Your more than likely correct ...

    but they still aren't rated from a liability standpoint ...
    most evaps like that I've seen are pressure rated at 150 to 300 psig .
    Dump a full charge in a room from a blowout and make people sick and see what happens when lawyers get involved....
    That will never happen .... Famous last words

    Absolutely no disrespect intended ,just my personal opinion
    They were only tested to that pressure since with R22 higher wasn't needed. Doesn't mean they could take more. And York and some other manufacturers admit they simply took their old r22 designed evap coils and retested them at higher pressure. they held, and they said ok, they're R410A rated. So a blow out wouldn't be as liable as you may think. As far as because it was from an "unapproved" coil. Same liability as a listed R410A coil.

    Why stick with R22, when its becoming more and more expensive.

  18. #38
    Join Date
    May 2002
    Posts
    949
    Post Likes
    Never said stick with R22,,,I said there are other options out there ....

    Being called in the office one day with several other techs and being told that we were being sued over something we considered frivolous , or no big deal, has made me a little gun-shy..

  19. #39
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by allstar08 View Post
    Well things were working well, then compressor noise started recently, and then mechanical failure. Looks as if Trane is having some problems with their 15 ton scrolls. The factory is running out of them, there have been several replacements around the country. I have to replace both compressors, Trane is covering the compressors, but not any labor allowance. Has anybody else run into this?
    Did you hear "looks as if Trane is having problems with their 15 ton scrolls" directly from Trane? Or is this wishful thinking/supply house rumor?

    I think your words above would have more street cred if these 15 ton scroll failures were occurring in brand new 410A systems (the entire system, including evap, coils, linesets) at a rapid pace, systems that had not been converted from R22. Perhaps they are, but I personally would be asking that question were I told "we're seeing a lot of failures with these 15 ton scrolls and the factory is running of them" with no other qualifiers.

    In your case I'm wondering if some time and $$ spent on RX11 flush may have made the difference between your scrolls failing or staying alive.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  20. #40
    Join Date
    Aug 2011
    Location
    Chicago
    Posts
    64
    Post Likes
    Sounds like a job bid by someone with just enough knowledge to put the car in Drive but not enough to check the brakes. Any AC DX job with an Accumulator or an Oil sep. Is a bad system wich has been band aided already suggest T&M only

+ Reply to Thread
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •