09-02-2012, 02:47 PM #40
Professional Member
- Join Date
- Aug 2011
- Location
- Chicago
- Posts
- 51
Sounds like a job bid by someone with just enough knowledge to put the car in Drive but not enough to check the brakes. Any AC DX job with an Accumulator or an Oil sep. Is a bad system wich has been band aided already suggest T&M only
-
09-02-2012, 10:49 PM #41
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
I heard it on this site and around the water cooler. I know what you are getting at, and I see your point. None the less I have heard mutterings about the compressors made south of the border and how they perform running 410. Why else would it take over a month to get replacements? I can call my local supplier and can count on my right hand how many times they have not had a compressor, including the three of these I have ordered.
If you read the Trane installation manual it does not recommend using R-11 flush kits.I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
09-02-2012, 10:54 PM #42
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
I can tell you love this stuff. Thanks for the input.
System has hot gas bypass and two txv's. Each txv has a check valve and a liquid line solenoid.
Compressors come with 1 1/8 equalizing line between them. There is a head pressure control, a Trane original, a damper controlled by an actuator on top of the fan discharge.I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
09-02-2012, 11:07 PM #43
Professional Member
- Join Date
- Aug 2012
- Location
- Tennessee
- Posts
- 62
Never let the customer, your company, or anyone else cause you to sacrifice your integrity and quality of work.
-
09-03-2012, 10:46 AM #44
Professional Member
- Join Date
- Jul 2008
- Location
- Nova-Scotia, Canada
- Posts
- 252
I find this thread very interesting. Everyone seems to be incredibly worried about the "components" not being rated for 410. I don't like Soft tubing running 410a, 500psi behind flares and new thin aluminum coils because they're cheaper to make but manufactuers seem to think this is still dandy. Are the coils 30 years ago really not rated for the higher pressures? Liability aside I'd be very interested to see if anyone has proof that the coils are (and I repeat in reality) not able to withstand 410A. As mentioned yes, not rated for 410 but when it the age where it was unrealistic to rate a coil for that pressure why would they?
I do understand the concern over liability and there is something to be said if another company (which can be compared to some of the worry warts in this thread) came in and started running their mouth about how it's not a 410 coil. Is type m copper? Is it still silphos? Yeah ok, if the coil is soft solder I understand. The evaporator and the existing piping is the only issue.
It's recommended (by dupont anyways) that it have no more than a 5% mineral oil left in the system. Drilling the traps was a good idea. Definitely changing the suction accumulator. My "personal" opinion is that this thread is filled with a slight air of hysteria but we all know what they say about opinions
. There is always the "absolute right" thing to do but frankly in some cases it's unrealistic in financial terms. You could have had a coil to match that air handler manufactured, repiped the entire run and done it that way but was that realistic? Is it still going to work in the fashion you described?
Time will tell.
-
09-03-2012, 01:30 PM #45
Professional Member
- Join Date
- Jul 2005
- Location
- Tulsa
- Posts
- 258
interesting thread....
-
09-03-2012, 01:38 PM #46
Professional Member
- Join Date
- Nov 2005
- Posts
- 1,311
I agree, I have never been concerned with the integrity of the components. I have been concerned with the need of the accumulator. The indoor coil is in the basement and the outdoor unit is about 8-10ft above it. I don't think we even need it.
I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
-
09-03-2012, 06:12 PM #47
Professional Member
- Join Date
- Mar 2011
- Location
- North Carolina Piedmont Area
- Posts
- 293
So what are you trying to say about preventing a future failure. Its obvious that he has an issue. It is true that its any one's guess as to why he has experienced such a sudden failure, but unless he covers the basics- it is guaranteed that it will happen again..
As for myself I am not concerned with the fact that its a mismatched system, however if the components are not compatible they must then be replaced. It is not likely that his piping is type "M" copper and most likely it is at least type "L".
There are not too many people here blurting.... just stating the facts.
To down play this situation at hand and to not give a positive solution is not "realistic".
Trouble shooting is not part of the repair..........understand the symptoms and you will find a solution.
-
09-03-2012, 06:56 PM #48
New Guest
- Join Date
- Aug 2012
- Location
- Columbus, Ohio
- Posts
- 4
Had a customer that did this. We gave them a quote to replace the evap coils but they went with a mom and pop operation that reused everything except the txv's. Well, 4 compressor replacements later I think it has finally run for 3 months straight. I noticed the suction line is always warm but I won't work on it because this customer is one of those that thinks " you touched it, its your problem now".
-
09-04-2012, 07:55 AM #49
Professional Member
- Join Date
- Aug 2011
- Location
- Chicago
- Posts
- 51
Salesman called me asked why i figured so much time to replace a compresser on a Desert Air unit. Says another shop beat us by 2k
"first I never saw it run, the customers maint. condemed it. Unit should be replaced. Every time I work there the Maintanence staff tells me how sharp they are and why am I here. Good luck to who got it" I figured 2 days for making it work right but go ahead cut the bid I'll slap a new Comp in and hit the button and walk away then wait for the customer wanting warranty after maint staff works on it.
-
09-04-2012, 09:56 AM #50
-
09-05-2012, 12:54 AM #51
Regular Guest
- Join Date
- Jul 2012
- Location
- Southwest
- Posts
- 114
I ran into this situation. Another contractor had the factory approve the huge slab coils from 22 to 410A. I went higher up and had it looked at and they said no. I quoted it the right way and lost out. Now its someone elses mess for life!
Didnt make the money from the job, but we also didnt risk the consequences of a lifetime of leaks.
Keep us updated if things start going bad?
You can also have a custom coil built once this one fails, etc.
-